Anyone converted a single stage gas atmospheric boiler to 2 stage?
Any preference for lo fire start controls? Pressuretrol or aquastat?
Or, is the usual to start Hi fire and then drop to Lo? (seems a lot easier-close on rise vaporstat and done.
Seems there are no changes with combustion air (fixed air shutters) for lo/hi on the atmospheric boilers I've seen, so is turndown determined just on combustion readings? I know with new boilers, they're all in the setup manual, how's that determined with a retrofit?
Any recommended materials to look at for these setups?
Used to be multiple (two) burners on some copper tube.
Raypaks had variable gas valve somewhat like a stove top.
In theory the former makes more sense.0 -
I was thinking putting a typical 2 stage gas train on the existing burner.Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.0
Since I did very little work on residential boilers I can only tell you what I have seen. How well they worked or how efficient they were is questionable. I have seen 2 stage and full modulating gas controls installed on these boilers. I was not impressed with how they worked but they were available for those that thought they needed them.0
I am looking into this -- there is some info here: https://forum.heatinghelp.com/discussion/comment/1265736#Comment_12657360
A "ghetto" solution is to use timer controls where the program predicts when short cycling is a risk and then shuts down the system for 30-60 minutes. So instead of a high-low solution you would have a high-off system. This would work as the radiators would be hot during the "off" period.
Located the timer solution. For me this would delay restart of the boiler for 30 minutes on really cold subzero days where my system begins to cycle on pressure (8 ounce cut-out).
https://forum.heatinghelp.com/discussion/182874/crazy-idea-pressure-triggered-time-delay
My next boiler will be Megasteam with Carlin EZ gas burner conversion and this timer1 -
Mine doesn't cycle on pressure, I'm thinking of adding a pressuretrol to go to lo fire at 4 oz or so.
Thinking of dropping input by no more than 40% so i don't get collapse of the steam at the end of the mains.Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.0 -
The reason I never considered it is the excess O2 on an atmospheric boiler is already too high by nature.
So lowering the gas pressure, to decrease steam output while increasing excess O2 and decreasing efficiency never made sense to me. You're literally making it run longer and less efficient. I'd rather run the boiler more efficiently and shut it off.
I did "convert" my EG-45 to an EG-40 by swapping the parts necessary to remove one burner tube but that kept it's efficiency where it's expected to be.
I have seen others who say the decrease in combustion efficiency isn't enough to matter and they could very well be correct. But I don't like it.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
That makes sense.
I think there are a lot of folks with converted vapor systems. They see their vaporstat short cycle on a couple of ounces and they are thinking man, my radiators are hot, there must be something better!0 -
cross_skier said:That makes sense.
A smaller boiler.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
I might consider this with an oversized boiler but @delcrossv if your boiler is not building pressure on a normal call for heat then I would leave it as is.
If you want to try this I would lower the gas pressure and combustion test it. See how low you can go and still have decent readings stack temp, Co2 and Co. You may find for what you gain that it is or is not worth doing.
Better than changing controls and gas valves and finding out your not much better off.1 -
@ChrisJ
In my case (cycling in subzero temperatures after firing for hours, more radiation would be the answer, not a smaller boiler) Boilers can always be downfired some.
I'm not a big fan of large steam radiators, adding more medium sized radiators is probably better.0 -
That's true.cross_skier said:@ChrisJ
@EBEBRATT-Ed Makes sense, part of this exercise is to lengthen the cycle time. I'll crank down the regulator and see what happens with the mixture. I do have a lot of slack with the burner shutters as it is now.EBEBRATT-Ed said:
Better than changing controls and gas valves and finding out your not much better off.Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.0
- 87K THE MAIN WALL
- 116 Chimneys & Flues
- 109 Geothermal
- 987 Plumbing
- 389 Solar
