Vaporstat gets stuck
1peterpan1
Member Posts: 5
Hello,
My steam heating system stopped working suddenly and upon further investigation I noticed that the flask with mercury in the Vaporstat Honeywell gets stuck in tilted position which prevents the system from working. When I touch or tap on the Vaporstat the flask tilts back and the systems starts working again. Please see the picture.
Any ideas on how to fix this? Do I have to replace the Vaporstat and if so which one should I get which is more reliable?
Thank you!
Thank you!
Looks like you've got a Pressuretrol, not a Vaposatat.
If the switch is not coming back on after the boiler pressure returns to atmospheric, it is likely because the "main" - the "differential" is less than zero. Try reducing the differential. If that doesn't work, then also increase the main, but just a bit (2 psi should be good.)
The scales aren't very accurate, so you really can't put much faith in their numbers.0 -
1st step is to remove the control and make sure the pigtail and the pipe connections into the boiler are clear of sludge. Also check the bottom of the control.
I just noticed that is not a vapor stat it is a regular pressure control0 -
And one other thing not mentioned above. The mercury type -- which is far more reliable than the modern microswitch type, by the way; don't lose it! -- is very sensitive to being level. Place a known high quality level across the top of the case and adjust the pigtail so it is exactly level.Br. Jamie, osb
Those usually have a hanging pendulum in the inside back on the right side.
There is a white dot of paint below for that to be lined up on.
As Chris L said, maybe a little more difference between settings also.0 -
In my not so humble opinion, Honeywell's L404A-1354 was their worst pressure control commonly encountered.
It is no longer made and good riddance.
I would remove it, dispose of the Hg properly (hazardous waste), and install a PA404A pressuretrol instead.
At least that is more or less adjustable to get it to work in the proper ranges.
I would also remove that steel pigtail and replace it with a brass pigtail.All Steamed Up, Inc.
https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc0
- 15.8K Strictly Steam
