CycleGard cycles constantly even when not heating.
JUGHNE
Member Posts: 11,466
I see how the term "Psycho Gard" came to be.
This is a CH 450 1560. This runs it cycle constantly 24/7.
So boiler might fire toward the end of the 15 minute cycle. Shut down for the 60 seconds but the tstat loses power during this 60 seconds and adds a few minutes of "Wait" time before calling for heat again.
So the total shut down time might be 4 minutes.
Any easy way to have it rest when not heating and start the 15 minute cycle when the heating cycle actually starts.
I assume not everyone changes these out.
Is there any way to start the timer cycle when the burner actually starts?0 -
My LWCO is no longer wired in before the thermostat, it's wired in after.
I'd recommend the same in the situation you described unless you at least get rid of the Cycle Guard.
This one is a 120 VAC unit.0
With 120 applied always to the LWCO, the 15 minute/60 second cycle is always running. So on initial fire you could be 14 minutes into the 15 minute cycle and get 1 minute of fire time before shut down.....which amounts to an actual 4 minutes to restart.
I&O for CG450 shows "SmartCycle" optional activation which used the "burner " terminal going to the orange wire on an oil burner control.
Where could and would this connect to a 24 VAC control system?0 -
How is it wired now? Does orange go to the transformer? Orange could power a relay that was in the safety chain for the burner although I'm not sure how I feel about some random relay being part of the burner safety chain.0