HB Smith Cast iron residential boiler tripping out on rollout switch
Comments
-
Either you putting too much gas into it, the boiler or flue pipe is plugged with soot or the chimney is not drafting.
Look up inside the chimney for blockages, the tile in the chimney may have broken down.
But a draft gauge on the boiler flue and see what you getting for draft. That boiler has a built in draft hood I think.0 -
I made sure the chimney was drafting and the flue pipe was completely clear. The gas pressure is spot on 3.5” w.c. The boiler does have a draft damper but I can watch the damper open up all the way and hit the end switch starting the ignition sequence. I suppose I can get up on the roof and look down the chimney just to be sure from the top down.
would turning the gas pressure down or trying to adjust the combustion air on the burners fix this issue?0 -
@kappy24
You can probably safely lower the gas pressure to 3" wc but you need to use a combustion analyzer.
If the fire is rolling out you have to find out why.
If you pour water into a funnel and it overflows what do you do? Pour faster or slow the pouring down? Same thing
What is your draft reading? You have to use a draft gauge and an analyzer0 -
HB Smith GB100 approx 19 years old never had a problem. now I have the same problem. Boiler heats up, but trips the Thermal Cut-off( roll out), above the burners, before it's satisfied. Flue appears ok, and I also have a gas water heater venting out the same chimney, with no problems. I have replaced the roll out switch, to no avail. I was wonering if it could be the Honeywell hi temp shut off. I could use some help……please…..Mark
0 -
To be clear — is this the rollout switch from the firebox, or the spill switch at the flue? Very different problems…
Probably be a good idea to get a tech. to clean the boiler and check all the combustion parameters…
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Roll out switch from the firebox
0 -
This. ☝️
Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.0 -
And it's past time to get someone out there and thoroughly clean the boiler, check the flue, adjust the gas pressures, adjust combustion…
Can't be done by eye.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 912 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements