Hartford loop
pipers
pipers Member Posts: 21
edited October 2021 in Strictly Steam
Why do we use a close nipple out of the tee on the Hartford loop
    EdTheHeaterMan Member Posts: 11,998
    You want the least amount of pressure drop. Some old drawings actually use a Y fitting instead of a tee.
  • delcrossv
    delcrossv Member Posts: 2,199
    Wye takeoff down to the wet returns?
    EBEBRATT-Ed Member Posts: 20,063
    @pipers
    In a Hartford loop you have condensate coming up a vertical return, crossing over the close nipple and going back down into the boiler. The equalizer on top has steam in it. The water and steam meet in the Hartford loop. A short (close) nipple or a Y fitting provides the shortest horizontal pipe which reduces banging and noise. If you use a longer nipple you could get a lot of banging
    pipers