Why do we use a close nipple out of the tee on the Hartford loop

Comments

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 2,215
    You want the least amount of pressure drop. Some old drawings actually use a Y fitting instead of a tee.
    Edward Young
    Retired HVAC Contractor from So. Jersey Shore.
    Cleaned & services first oil heating system at age 16
  • delcrossv
    delcrossv Member Posts: 29

    You want the least amount of pressure drop. Some old drawings actually use a Y fitting instead of a tee.

    Wye takeoff down to the wet returns?
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 9,616
    @pipers

    In a Hartford loop you have condensate coming up a vertical return, crossing over the close nipple and going back down into the boiler. The equalizer on top has steam in it. The water and steam meet in the Hartford loop. A short (close) nipple or a Y fitting provides the shortest horizontal pipe which reduces banging and noise. If you use a longer nipple you could get a lot of banging