Hartford loop
pipers
Member Posts: 21
Why do we use a close nipple out of the tee on the Hartford loop
0
Comments
-
You want the least amount of pressure drop. Some old drawings actually use a Y fitting instead of a tee.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Wye takeoff down to the wet returns?EdTheHeaterMan said:You want the least amount of pressure drop. Some old drawings actually use a Y fitting instead of a tee.
Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.0 -
@pipers
In a Hartford loop you have condensate coming up a vertical return, crossing over the close nipple and going back down into the boiler. The equalizer on top has steam in it. The water and steam meet in the Hartford loop. A short (close) nipple or a Y fitting provides the shortest horizontal pipe which reduces banging and noise. If you use a longer nipple you could get a lot of banging1
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements