Hoffman 70A
delcrossv
Member Posts: 2,199
How does the 70A compare to the 40- faster, slower? (not listed in the guide to vents)
It's twice the price, so I'd like some guidance before I get some.
Thanks!
Thanks!
Slightly slower. ISTR it's more expensive because it is built to military specs.All Steamed Up, Inc.
Consulting1 -
The difference between the #40 and 70a valve is the operating pressure.
The 70a is good to 15 psi max and the 40 is good to to 10 psi max.
In a normal operating system in lower pressure applications such as systems that operate at pressures under 5 psig I would certainly use the #40 vent valve. There is no difference in the air discharge rate that would be meaningful.
JakeSteam: The Perfect Fluid for Heating and Some of the Problems
by Jacob (Jake) Myron1
- 117 Geothermal