Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Buderus propane boiler shutting off randomly

CCouture65
CCouture65 Member Posts: 2
Buderus propane boiler shutting off randomly weeks apart at a time. I then hit flume temperature reset button then starts up again no problem. Gas company switched out sensor, adjusted temp setting on boiler to 180, still having problem. Chimney is clear of debris. Flume is open when running. Just hate to call company out for third time and still not have it fixed looking for any suggestions?

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 23,276
    Has anyone done a thorough combustion and draught test?

    Have you ever caught it in the act? Possible momentary drop in gas pressure?
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • GW
    GW Member Posts: 4,692
    Been there, short chimney? 
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
  • JUGHNE
    JUGHNE Member Posts: 11,060
    Is there enough combustion air available?
    Tight room?
    Water heater in the room?
    Clothes dryer or exhaust fan sucking air out of room?
  • CCouture65
    CCouture65 Member Posts: 2
    I have not done a combustion test as of yet. The boiler is in a large open space with a water heater and dryer in same room/general area. As far as a short chimney, if it was too short would that cause a decrease in the draft and cause to overheat and flip temperature sensor? Thanks for all the suggestions and help!
  • Jamie Hall
    Jamie Hall Member Posts: 23,276
    Ah... yes a shorter chimney could reduce the draught, but that's adjustable.

    You really won't have any idea at all until you do a full scale, comprehensive combustion test and adjustment.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • GW
    GW Member Posts: 4,692
    Yes. Short is little draft, tall is lots of draft  
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com