Mass. oil tank code
Paul_69
Member Posts: 251
in Oil Heating
If a oil tank inside a building in mass. was less than 5Ft from a oil burner, is it in the code that you could put up a fire wall?
0
Comments
-
Yes, according to NFPA 31, which I think Mass now uses. Can't remember if it has to be a 1 hour or 2 hour wall construction.steve0
-
Yes, Ma gave up their own oil burner code and now follows NFPA 31 from what I understand.
Funny thing is most of the installers don't know this. MA passed the new law in 2015 I think and never notified anyone. I only found out when I called the state fire marshalls office to ask a question.0 -
-
Thanks for the info guys!!0
-
Just so you know.NFPA is the current “Recommendations “
thats Minimum.0 -
I believe MA adopted NFPA31 2011, so changes since then don't necessarily apply.To learn more about this professional, click here to visit their ad in Find A Contractor.0
-
MA did adopt NFPA 31 in January of 2015 I believe. Funny thing is no one in the state seems to know this. They never told anyone. I used to teach at the union hall and they were still teaching oil burners on the old MA Code.
The only reason i found out was I called the State Fire Marshall to ask a question0
Categories
- All Categories
- 85.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 424 Carbon Monoxide Awareness
- 72 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 129 Geothermal
- 160 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 878 Plumbing
- 5.9K Radiant Heating
- 375 Solar
- 14.6K Strictly Steam
- 3.2K Thermostats and Controls
- 58 Water Quality
- 49 Industry Classes
- 89 Job Opportunities
- 28 Recall Announcements