Air Vent on Steam Radiator Won't Stop Hissing
About two days ago (nearing the end of our heating season), the air vent on my main steam radiator started hissing without regulation, meaning it just keeps going when steam is flowing. I can't visibly "see" steam coming out, but I can feel and hear it.
I imagine this is a straightforward problem as it just started, but I couldn't find a resolution on this page. I'm not sure if it means it just needs to be replaced, but thought I would ask before testing random amateur ideas out there.
Any and all advice is greatly appreciated!
  • ColdNights
    ColdNights Member Posts: 21
    I also checked and the boiler is at proper psi with and the sight glass looks as expected
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,578
    How many ounces is your pressure?—NBC
    EdTheHeaterMan Member Posts: 11,577
    My guess is the vent just failed. See if you can replace it with an identical model vent.
  • neilc
    neilc Member Posts: 3,129
    and a quick picture of the boiler, gage, Ptrol, and pigtail
    is the gage after the pigtail, with the Ptrol?
    or are they separate?
    known to beat dead horses
  • ColdNights
    Thanks! It is at/below 2 psi.
    Is that pressure measured on the 0-30 psi gauge?
    It may not be accurate at the lower pressures needed for these systems. Best would be a 0-3 psi gauge, on a tee with the pressuretrol, and the original gauge.—NBC
  • salesnyc
    salesnyc Member Posts: 2
    I have the same problem. I’m a heating professional and can’t figure it out. Only one radiator is non stop venting. Replace the air vent with two new ones of the same kind. Maid-o-mist and still venting non stop. Pressures under 2psi.
    EBEBRATT-Ed Member Posts: 19,602
    @salesnyc
    What is it venting? Air? Steam? Or is it sucking in air? What model vent?
    ethicalpauldabrakeman