Capacitor under load testing
AtifMahmood
Member Posts: 1
What is 2652 while we are testing capacitor under load
What procedure are you using to test the capacitor?0
what? You can calculate the capacitance by measuring the voltage across the cap and current through it.0
You know, I'm rarely really baffled by a question, but that one's got me. It's utterly meaningless as posed. Try again.Br. Jamie, osb
He's measuring amperage of the start windings multiplied by 2652 then divided by the voltage across the capacitor to get the actual capacitance while the system is running. Its a more accurate way to test a capacitor than using multimeter, because you are measuring using the voltage that the system is operating with. I've seen capacitors that check out ok with a meter fail the test outlined above. Using this method on maintenance calls pretty much eliminates failed dual capacitor service calls for our maintenance customers.PC7060 said:What procedure are you using to test the capacitor?
I'm not sure where the 2652 comes from. I'm sure it relates to Ohms law in some way.3 -
The actual number is not 2652 but it is close enough. It is easy to remember because 26 + 26 = 52
this is from an article in ACHR News.
"Since I started training with this method, I have often been asked where this calculation comes from. It is actually a simplified version of the equation to find capacitative reactance combined with a version of Ohm’s Law: Xc = 1/(2 x π x ƒ x C) and E = I x Xc.
I’m taking the 1/(2πƒ) part, multiplying by the measure we’re looking for (microfarads or millionths of a farad). This gives us the capacitative reactance, which, multiplied by the amperage and then divided by the voltage, gives us the capacitance. So you get: Xc = 2,652 and E = 4.4 x Xc = 11,668.8, so that 11,668.8 ÷ 335 V = 34.83."
Perfectly understandable. Clear as Mud!
"To simplify, we can use approximate numbers and just call it amps times 2,652. Then, divide by the voltage."
Read the full article here https://www.achrnews.com/articles/135163-testing-the-run-capacitor-while-the-system-is-running
This goes under the "He forgot more about HVAC than you will ever know" department and I just go with it.
Respectfully Submitted,
Mr.Ed
PS. sounds like @AtifMahmood is the type of person who needs to know why it works. Not just that it works. I believe we need more analytical minds in this industry. Seems that the Trades get the people that are considered Sub Standard by those from Yale and Harvard, or who work on Wall Street. Little do they know that without the Trades, they would not be able to take that elevator to their corner office.
I digress, but I applaude AtifMahmood. Keep asking those questions. Learn as much as you can!
4 -
The farad was named in honor of Michael Faraday. I believe there is also a restaurant chain named after him. TGIFmattmia2 said:it comes form the definition of a farad and some algebra...
I could be wrong on that restaurant thing
3 -
I HATE formulae like that. It's a compilation of a number of constants -- with a couple of assumptions. Yes, it works. But -- it assumes the frequency is 60 hz, so it only works in North America. And it assumes that you want the answer in microfarads, which you usually do... but not always.
And I might point out that it would work for either the start or run capacitors (assuming there are two) -- but only when they are in the circuit when you measure the current.Br. Jamie, osb
The constant really should always be written with the units and the user should cancel the units out. It doesn't solve the problem with the impedance being dependent on frequency, but it helps with most other errors.Jamie Hall said:I HATE formulae like that. It's a compilation of a number of constants -- with a couple of assumptions. Yes, it works. But -- it assumes the frequency is 60 hz, so it only works in North America. And it assumes that you want the answer in microfarads, which you usually do... but not always.
Thanks Ed for the explanation
I’ll make a note and start testing on the fly0
- 120 Geothermal