Member Posts: 1,457
I have a customer with a water boiler that I think when it shuts off it bangs almost sounds like a steam boiler bang when the steam hits the water..................or when a zone valve closes but it’s three pumps ( taco with ICV 007 ) 2 baseboard zones and 1 radiant floor I all get measurements later but I think linier feet it’s about 120 feet including return to boiler.
If it was air would I be hearing it all the time like an ocean.
If it was air would I be hearing it all the time like an ocean.
0
Comments
-
When a water boiler bangs it's because it's boiling internally which is created by a lack of flow. Check your pumps and back off of your aquastat 10° or so and then reassess.Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
What boiler is it? Make/ Model?
0 -
Thanks John, I will back off the aqua stat and see what he get.
kc, it’s a Utica 80 % standard in chimney , but I look later.0
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 114 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements