Has Furnace Fails to Ignite Intermittently
Gumby77
Gumby77 Member Posts: 22
https://youtu.be/9a-LrE7eq2k
The draft inducer on my furnace sometimes starts and stops before the burner and blower finally go. Other times the furnace works perfectly normal. This is a Lennox 193UHE. It's only a couple months old and in a new house. No other exhausts on the furnace pipe. I have replaced the honeywell thermostat with a nest but the problem was there before the switch. I have changed the thermostat recently but the problem was there before that change.
    HVACNUT Member Posts: 7,436
    New house to you or new construction?
    At only a couple months old, the installer, and or GC is responsible.
    Why are you here? Have you contacted them?
    Gumby77
  • Gumby77
    Yeah it's new construction. I'm going to contact them Monday. It was pretty cold here this weekend and I just wanted to kick start things just in case it went out and I couldn't get anyone in here right away. I really like learning about issues so at least I'm familiar when the pro comes in, plus it's good knowledge for future reference. Thanks.
    EBEBRATT-Ed Member Posts: 20,166
    Sounds like your original installer should take care of this.
    On a call for heat the draft inducer starts first
    Then he hot surface ignitor glows
    then the burner starts
    then the main blower comes on
    Check the flue pipe for any obstructions, could be the pressure switch that proves that the inducer is running might be faulty or it's connections plugged.
    Is this a high efficiency furnace with PVC exhaust pipe?
    Make sure the condensate drain is clear and the furnace isn't holding water
    But in any event you need a professional to look at this
    LS123
  • Gumby77
    I've had hvac company out 4 times. They've replaced the control board, pressure switch, gas valve and inducer motor to no avail.  It still throws code 11 "pressure stuck closed prior to inducer motor startup". I continually bring up the condensate piping to them cause the pitch of the piping after the trap is negative and it holds water in the drain pipe. I noticed also that there is no vent tube on the vent outlet of the trap. The instructions explicitly state vent tube must be minimum 1" above condensate outlet and max of 2" above. My wisdom is could this cause issues with the pressure switch? They don't seem concerned with this.
    pecmsg Member Posts: 7,056
    Where's the pipe that goes up from the "T" go to?
  • Gumby77
    Sorry I should have labeled that. That is the drain from the ac evaporator. There is another vent above this for that drain line.