I recently bought a home with an oil furnace. Many of the pipes on the furnace were bad so I had them replaced, a new transformer installed, and had new thermostat wire ran. (All by an HVAC friend of mine) After the work was done, I noticed an issue with one of my two zones.
Which zone valve do you have.
Power off.
The simple check is to take the wires off the zone valve terminals that are on the end switch. Depending on whether you have a 3 wire zone valve or a 4 wire zone valve.
Connect the 2 wires together.
Power on.
If the burner fires it's the zone valve or the wires powering it. If it doesn't fire the burner, it's the wiring between the zone valve and the aquastat.There was an error rendering this rich post.
@STEVEusaPA its a 4 wire I believe.
The other thing I should mention is the motor itself is very very warm. The old motor as well. The valve itself is not warm, but the motor is too hot to touch for more than 5 seconds.
Ok so I jumped the red wires and the burner did not fire0
I hope you didn't jump the red wires on the zone valve but the red wires they were connected to.
Time to trace some wiring. Many times with thick and thin wire under the same wire nut, there's a loose connection, or no connection.
I'm surprised your hvac 'friend' is leaving you hanging.
In the meantime you can take the power leads off, and open it manually. When the other zone calls both will heat up. Until you get it fixed.There was an error rendering this rich post.
I did connect the wires connected to the zone valve. I thought that sounded off. I’ll redo it and connect the right wires. Thank you0
Different zone valves have different wiring diagrams. Your problem may be incorrect wiring or it could be a defective part. Can you tell if your zone valves look like any of these common valves? If it is not one of these can you post a picture of your zone valves?
Some are easier to understand the wiring than othersEdward Young Retired
Actually, the red wires coming from my zone valve are connected to the red wires on the adjacent zone valve. Both of these wires are connected to thin thermostat wire that runs to the aquastat0
I bought the entire zone valve so I have more than just the motor. I could swap the whole head to eliminate the possibility of bad parts.0
If you twisted the 2 wires going to the aquastat together (remove the zone valve wires), and the burner doesn't fire, it's the wiring. If it does fire, it's the zone valve. Because the other zone valve works correctly, I wouldn't think it's the aquastat.richkenny7 said:Actually, the red wires coming from my zone valve are connected to the red wires on the adjacent zone valve. Both of these wires are connected to thin thermostat wire that runs to the aquastat
You can also check the 2 leads for the end switch coming off of the zone valve. When powered, you should have continuity (the end switch is closed). If you have continuity, again, it's the wiring or connection between the zone valve and the aquastat.
You can use your meter to check continuity between all the low voltage wiring (power off).There was an error rendering this rich post.
@STEVEusaPA I connected the two wires coming off the aquastat and it fired.No continuity on the end switch wires. Is that my problem? Bad end switch?0
Ok so I swapped the whole head and problem solved. Thank you very much @STEVEusaPA @EdTheHeaterMan. You guys are amazing for offering your help and knowledge. I shall name my first born Edward Steven!!
@HVACNUT that’s what I did and it fixed it. I should’ve done that first, but at least now I learned about end switches and how to test and I know that my old motor is still good so I have a spare. Thanks man!1
LOL. Hay Steve... looks like I get first billing 🤪richkenny7 said:Ok so I swapped the whole head and problem solved. Thank you very much @STEVEusaPA @EdTheHeaterMan. You guys are amazing for offering your help and knowledge. I shall name my first born Edward Steven!!