Have to turn T-Stat all the way up for Upstairs to Heat
Dairon421
Member Posts: 81
So here is the situation guys. So a customer has a single family house but Renting out the upstairs and downstairs with only 1 steam boiler heating system. The first floor is not occupied but the thermostat is on that floor. Upstairs Tenant have adjustable radiator valves and they all set 5 which is the maximum setting. But the problem is he have to set the boiler up all the way to 87 for the radiators to get warm. Can you give me all the possibilities on what could be going on?
What is the actual room temperature on the first floor with the thermostat set on 87? it may be as simple as your thermostat is faulty, or getting an inaccurate reading (steam pipe in wall behind thermostat, etc).0
84 degrees0
If the TRV's are on the air vents of a single pipe radiator. They will shut of the air vent and not reopen until the boiler shuts down...with your tstat at the 87 setting the boiler may not shut down for the 2nd floor to reset to heat again.
But at 87 I suspect the pressure control should be shutting the boiler down.
What is the pressure on the boiler.....clean pigtail....pressure control settings??1 -
The best approach to this -- which may not be possible with tenants -- is to take the TRVs off all the radiators, and set about getting the heat even by altering the venting as needed. You may find you need to slow the downstairs venting a good bit. If you have inadequate main venting, that doesn't help.
Then once you get the venting correct and the heat even, upstairs and downstairs, you can consider putting the TRVs back on -- but remember that they cannot increase the heat in a space, only decrease it.Br. Jamie, osb
I solved the problem. The problem was we had 2) bad main return vents in the basement and none of the steam piping was insulated. I changed the vents and insulated the lines. Also there was a big radiator in the same room as the thermostat. I put a adjustable radiator valve on that radiator and put it on the low setting so the thermostat don't turn off so quickly when the upstairs start getting warm. No complaints after doing that.