Wiring CAS-4JR Combustion Air System with multiple zone valves
shredmaster
shredmaster Member Posts: 30
edited January 2021 in THE MAIN WALL
this is my existing setup, with tt that go to the weil mclain CGA5 boiler. everything is wired like the diagram (pic #1)below and I need to add a CAS-4JT combustion air system (pic #2).
Base on my understanding, the sequence should be as below.
Thermostat -> CAS-4JR -> zone valve -> TT
If there is one zone valve/thermostat, I can wire T1 to common, when the thermostat calls for heat, the W/Y (thermostat) send to T2, then send T3 to the W/C (zone valve).
but how would you wire this with a 3 zone valve and thermostats? there is no way for T3 to know which zone valve should get the return (TH) wire.
thanks in advance!
  • Solid_Fuel_Man
    Solid_Fuel_Man Member Posts: 2,644
    Wire the end switches (all in parallel as shown) the the combustion air, then the combustion air to the tt on the boiler.
    Sequence would be:
    Any thermostat => respective zone valve end switch => CAS => boiler TT.
    Does that make sense?
    STEVEusaPAshredmaster
  • Ironman
    Ironman Member Posts: 7,859
    edited January 2021
    Here’s a simplified drawing. T2 must connect to the common side of the boiler’s Transformer.
    Bob Boan
    STEVEusaPAHVACNUTEdTheHeaterMan
  • shredmaster
    edited January 2021
    Sequence would be:
    thanks for reply, that's what i end up doing. here is how everything are wire together in case anyone might be interested.
    C (transformer common) -> CAS T2
    Transformer R -> Zone Valve Endswitch T1
    Zone Valve Endswitch T2 -> CAS T1
    when Endswitch is closed, the CAS will close the relay and turn on the fan, then send Transformer R to CAS T3
    I bought a 24v relay switch from amazon, wire the green to C, black to CAS T3, then hook up with NO to boiler TT.
    this relay is unnecessary per @Ironman drawing.
  • shredmaster
    edited January 2021
    simpler than what i end up doing and I can return the relay. thanks for the drawing, I didn't know the T T is just the R side of the transformer.
    EdTheHeaterMan Member Posts: 11,575
    edited January 2021
    Just think of the end switch as the thermostat on a single zone system. On a call for heat the end switch contacts close moments after the thermostat contacts close. Since all the end switch contacts are wired parallel to the TT on the boiler, then any of the zone end switches will act as a thermostat would act.
    You just need to know which of the Boiler TT is the “Red” or T1 or R or Power terminal and which is the C or Common or Return path to the Power Source (or in some cases Chassis Ground.)
    Yours truly,
    Mr. Ed
    Solid_Fuel_Man
  • shredmaster
    Yours truly,
    Mr. Ed
    I have CGA5, how do you tell which boiler TT is the power terminal which is the C?
  • shredmaster
    edited January 2021
    I just follow your diagram and was able to wired the CAS without the relay switch i got from amazon. I notice a small issue, when ES closed and boiler closed the gas valve after reached the temperature setting, the fan still kept going. would be ideal if fan only runs when ES is closed and boiler is also firing. here is the schematic wiring diagram for my CGA 5, can that be done?