York Furnace P3UGD16N09001B (Circa 1989) with AC

MelR
MelR Member Posts: 1
This model uses a S1-02521911701 transformer that has the wiring block integrated with it that is fried with 120V present on the primary side and 0V on the secondary side due to a short and so I have ordered a new one. The current tstat is the original mercury tube one using only R,G,Y,W terminals. What is confusing to me is that the wiring block has nothing attached to its Y terminal and the Y wire to the tstat and two heavier gauge wires attached to the C terminal. I wish to change out the tstat to a programmable one that needs a C wire for constant 24V. There is a spare blue wire in the loom, but it doesn't have continuity to the tstat end, so I wanted to go with the add-a-wire kit to be able to end up with the new stat. When I tested the wiring at the block before the short, I saw 24V between R and W, R and W and R and G, 0V between R and Y. How the heng should the wiring block be wired and why was the block wired this way?

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • JUGHNE
    JUGHNE Member Posts: 11,444
    Do you have AC and a tstat with AC cooling switch?
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 18,016
    If you get the same part:
    R on the term block goes to R on the thermostat
    C (common) on the term block goes to C on the thermostat
    Y on the terminal block goes to Y on the stat
    G on the terminal block goes to G on the stat

    You will have other wires on those same terminal block connections. Leave them alone or reconnect them as they are now
  • Big Ed_4
    Big Ed_4 Member Posts: 3,226
    On the older single speed furnace Y terminal was just bug or connection screw to connect wire to condenser. You did not need to connect to Y at the airhandler . Today the Y would put the fan on high speed as well as powering a contractor in the condenser and the wire back from condenser was connected to common for the contractor .