York Furnace P3UGD16N09001B (Circa 1989) with AC
MelR
Member Posts: 1
in Gas Heating
This model uses a S1-02521911701 transformer that has the wiring block integrated with it that is fried with 120V present on the primary side and 0V on the secondary side due to a short and so I have ordered a new one. The current tstat is the original mercury tube one using only R,G,Y,W terminals. What is confusing to me is that the wiring block has nothing attached to its Y terminal and the Y wire to the tstat and two heavier gauge wires attached to the C terminal. I wish to change out the tstat to a programmable one that needs a C wire for constant 24V. There is a spare blue wire in the loom, but it doesn't have continuity to the tstat end, so I wanted to go with the add-a-wire kit to be able to end up with the new stat. When I tested the wiring at the block before the short, I saw 24V between R and W, R and W and R and G, 0V between R and Y. How the heng should the wiring block be wired and why was the block wired this way?
0
Comments
-
Do you have AC and a tstat with AC cooling switch?0
-
If you get the same part:
R on the term block goes to R on the thermostat
C (common) on the term block goes to C on the thermostat
Y on the terminal block goes to Y on the stat
G on the terminal block goes to G on the stat
You will have other wires on those same terminal block connections. Leave them alone or reconnect them as they are now0 -
On the older single speed furnace Y terminal was just bug or connection screw to connect wire to condenser. You did not need to connect to Y at the airhandler . Today the Y would put the fan on high speed as well as powering a contractor in the condenser and the wire back from condenser was connected to common for the contractor .
There was an error rendering this rich post.
0
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 925 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements