Buderus G115WS/4 / Carlin EZ-1: lockout during TFI
operation, time does go by quickly...) two weeks ago. The heating guy said
we should do it more often, but didn't say it was particularly dirty. My
pellet stove is the primary heat for the house, and I use a heat pump
during the summer for DHW, so the oil doesn't get used too much (at least
compared to some...) ~400 gallons of oil a year. It was working fine
before that, I just figured that I should get it cleaned.
It ran fine for the next two weeks; I didn't notice it running any
differently or anything. Today, I don't have any hot water, so went to
look at it, and it is lockout. I reset it and I can hear the flame turn
on, and it sounds normal (as far as I can tell, I don't think there is a
place for me to look at the flame, which would be useful), but the CAD
sensor doesn't see the flame, so turns off.
I took out the ignitor and nozzle, and there was a bit of thin black stuff
to be wiped off the nozzle and elsewhere, but nothing that looked
concerning to me (I was hoping to see a glob of something that would be
obvious). I measured all of the distances and the ignitors are at 5/64"
(manual recommends flush to 1/16"), and I tried to adjust it, but the
ignitors are blocked from sliding back farther by the ceramic block that
holds the wires, but maybe that isn't important.
I put it back together and I think maybe I didn't get it seated into the
hole very well, as then it didn't light properly (heard the igniitors, but
the actual burn noise/whoosh was pulsating and not normal. It turned
itself off (quicker than before) and then I thought well maybe it is
because there is air in the line since the tube emptied out when I took it
apart, so I reset it, and the pulsating noise was better, but still not
quite normal. It turned itself off again and then started smoking within
a few seconds. A minor amount of smoke, in hindsight, I think I didn't
get the nozzle seated well and fuel vapor was coming into contact with
heated parts after it is shut down and turning to smoke instead of
igniting.
I reseated the nozzle/ignitors, and it is working better, but the CAD
sensor still isn't seeing the flame.
The CAD sensor ohms out properly with darkness and daylight. It had a bit
of fuel inside the sensor (outside the glass cover), so definitely fuel
has been spraying around improperly. There is some wetness in the air
tube, though it isn't growing, so I think that was from the first time I
seated the nozzle.
Googling around, I find some people talking about different nozzles that
appear equivalent, but actually aren't, Hago ES vs Devalen B; I currently
have a nozzle labeled .60, and the heating guy wrote both names on the
paper, so I'm not sure which one I have (and I don't know which one I had
before).
The cleaning guy didn't put the cover on properly - there are two clips
that hold on the hinged top plate, and he had one clip under the gasket,
so there was at least an air leak for the last two weeks, and also broke
off the plastic clip that holds the primary control, the air intake
adjuster is noticeably dirty, and he didn't replace the oil filter. (I've
replaced the oil filter once, a few years ago). So I'm not thrilled with
his service.
And of course, now that it is Thanksgiving, I'll probably have to pay for
a holiday service fee if I have someone come out today.
Given that I have a pellet stove, I can probably get by for today; it
isn't too cold outside yet.
Any ideas?
Thanks. Happy Thanksgiving!
Homeowner
Buderus G115 / Carlin EZ-1 Oil burner
(6 zones: DHW, 2 radiant, 3 baseboard)
Pellet Stoves: Kinderhook FS, Kozi KSH-120 (6 tons)
Heat pump for summertime DHW: Nyle Geyser RO ($8/month)
Solar air heaters: 8 replaced $750 of propane annually
Yes, call the heating guy back. You really shouldn't be playing with the burner, especially considering what happened when you didn't "get the nozzle seated well".jondaley said: Any ideas? Thanks. Happy Thanksgiving!
It needs service by a professional. If they're worth it, they offer holiday emergency service. You don't have the equipment needed to properly diagnose and repair the burner. How will you know its burning a 0 smoke?
I understand the boiler doesn't get used much but you glossed over the fact that it sat neglected for 9 years. It should be at least checked/tested every 2 years even with limited use.
Did the tech do a combustion test and leave a printed copy of the report? If no, then call someone else.3 -
Yikes. Sounds like you need to find a new oil service technician. Someone who is familiar with the use of a digital combustion analyzer and tuning a burner properly. This guy sounds like a clown.
Please don't mess around with it, oil burners aren't something that should be attempted DIY. You can easily make a problem worse and cause the boiler to soot up and possibly cause a puffback.0 -
400 gallons of oil a year and this is your backup system? I burn 550 to 600 gallons of oil a year to heat the house and all my DHW And yes that boiler and flue pipe get brushed ever year , filters and nozzle changed, and combustion checked . 9 years is way to long for a tuneup. And yes I hire a pro to do the work . The cleaning and tune up fee each year is cheap money to keep a ten thousand dollar system running efficiently and reliably . Now if only my vehicles could be maintained for that small cost
2 -
@HVACNUT He did leave a report. It matches the one from the initial install.
@jimna01 yeah, it's big house (~6000 sqft of insulated/heatable space, plus another ~2000 sqft of attic and basements) that was built 140 years ago. The last owners used 2500 gallons a year, so I've improved the situation a lot with this new fangled stuff called insulation and air sealing. And here in NH, people are used to fairly high heating bills, so my bills aren't that bad (6 tons of pellets, 300 gallons of oil, 30 gallons of propane).
Homeowner
Solar air heaters: 8 replaced $750 of propane annually0 -
Some oversights to say the least. The ws/115 is an upfired version of the 115. Blended fuels don't lend themselves to the higher pump pressures.
Stratification with bio blend is possible.
Get a fuel delivery after service? Fuel quality has been a big problem lately.
The least expensive fuel company tends to have the highest amount of bio. However, have seen greedy dealers selling bio at a premium.
@BDR529 hmmm. I hadn't thought about oil delivery. I have a new supplier who is new to town and undercutting everyone else's prices. I figured it was because they were new, so are desperate for customers but I wonder if your thought is correct and they are delivering a different fuel. I will ask around if anyone else is having problems along those lines.
I got a small delivery to top off the tank just before the service. 50 gallons I think.--
Homeowner
It’s probably not the fuel. It worked fine for 9 years, got serviced and doesn’t work now.
You shouldn’t have touched it yourself. Call the company who did the service and get them back out there.
Let them know what it was doing, what you saw and what you did.
It’s either going to cost you, or you get a cold shower until tomorrow.There was an error rendering this rich post.
Hardly any of this is true.BDR529 said:Some oversights to say the least. The ws/115 is an upfired version of the 115. Blended fuels don't lend themselves to the higher pump pressures.
“Blended fuels don't lend themselves to the higher pump pressures“.
Says who? Higher pump pressures and bio are used through the world with no problems.
“Fuel quality has been a big problem lately.”
Where? Companies trying to store their own fuel, blend their own bio, especially with non spec bio is the problem.
“The least expensive fuel company tends to have the highest amount of bio.”
Makes no sense.
3 -
I see this more and more every day the tech doesn’t have a clue what he’s doing or doesn’t care the problem is the residential customers are cheap and it’s ruining the industry no one wants to pay for the job to be done right. This is why I do mainly commercial work now
Don’t mess with it any more the more you do the longer and more expensive it will be to fix I don’t want to sound like a **** but when I get called out to this sort of job on and a what would have been a quick fix now takes 4 hours because I have to readjust head position because someone messed with the adjustment plate and now I have to pull the burner to reset and clean 5 lbs of soot out of the boiler I have to charge for my time and it gets expensive quick.
2 -
Everything I said is true. Because someone has blinders on dosen't change the fact.STEVEusaPA said:
Makes no sense.0 -
Who has blinders on? Present you facts, instead of blanket statements.
Your statements could simply be based on what your company is doing incorrectly and don't reflect the market as a whole.There was an error rendering this rich post.
Alright, I figure you are in PA. I'm in Boston/ Southern NH The fuel we got up here is junk sold by SOME dealers. It is a problem that has to be addressed on no heat calls.STEVEusaPA said:Who has blinders on? Present you facts, instead of blanket statements.
I guess I'm the only one that has these problems with the fuel. Well, shame on me.0 -
Not too many years ago when bio fuel blends were new and on the rise, awful things happened with fuel delivery to the burner.
I must admit Sir, you have let things go too long.
Some things I have done for a long time have diminished clogged fuel lines and, for me, have eliminated fuel related service calls.
Add one or two more filters to the line. The first would be a yarn type FB4 right out of the tank and next a 10 micron spin on filter.
Blow out the lines with compressed air and thoroughly flush until clear. If the line does not clear up well, add a third filter at or near the pump. (You have told the customer the pitfalls before servicing, had them sign the work order too).
Thoroughly flush the line mechanically, replace the pump strainer and clear the high pressure port also. Set the pump pressure high, like 175 psi. I never have any trouble with light off or operation with this method. Just be sure to down size the nozzle correctly.
Flue passages are cleaned as well as the pipe. Chimney is checked or power venter, if used, is disassembled and cleaned
Everything is checked. Any issues noted and reported.
System run and combustion checked.
I am very thorough with my service.
This takes between 2 and 4 hours. If customers don't like my estimate, I tell them to go with the cheaper guy. Cheap isn't good, good isn't cheap.
It is my duty to provide a professional service to my customers. I've been doing it like this for 44 years and have a good following, I'm happy to report.2 -
My heating guy came and fixed a couple things - the first heating guy had positioned the points incorrectly, and calibrated the air flow for warmer air, so I as I suspected, the first night of cold air caused problems.
So, it wasn't burning very cleanly, and then he also replaced the CAD sensor, which must have been borderline, so even though it ohmed out correctly, the flaky burn flame was enough to make it not sense the flame entirely, and caused it to lock out.
I didn't know about the pretty cover on the Buderus that was covering up the window where I could have seen the flame, so I'll be able to check the flame quality next time.--
Homeowner
Its impossible to check "flame quality" by looking through a window. I never clean the window. For spite.jondaley said: I didn't know about the pretty cover on the Buderus that was covering up the window where I could have seen the flame, so I'll be able to check the flame quality next time.
Did your heating guy happen to leave behind a copy of the combustion report?0 -
The first guy did; I'm not thrilled that the second one didn't, but the second guy made it actually work. And his setting matches what the manufacturer recommends.
I understand you can't calibrate efficiency by looking at it, but it makes sense to me that you can tell the difference between a starving for O2 vs too much OF by looking at it.
And in this case, as soon as they took off the cover, it was obvious something was wrong with the flame and after adjusting the intake O2, it burns nicely.--
Homeowner
Lockout during TFI tends to mean "no oil". For the Carlin 70200 controller, it is worth looking at the error logs. The error messages may indicate "No flame" and immediate lockout. The burner run time will be == the configured TFI secs +1. If it is the solenoid, the error message will be "No flame, check vlv", likely you will also see some "recycle"-s, with the "valve amps low" flag, and "Lost flame" erro message. If you rule out the solenoid based on the error logs, it is most likely that it could not establish flame during TFI, because there was simply no oil for another reason. Why? Rule out a clogged nozzle, or clogged filter. Easy and inexpensive to replace both. Make sure the tank is not empty.
The reason I am rather familiar with the details of the different errors, is debugging "intermittent lockouts".Everything seemed to be OK, yet intermittent "No flame" lockout occurred..
But, only during cold weather, and only if the heating system was idle for a few hours. I figured it was a slow air leak somewhere in the line, close to the burner. Given enough idle time, all oil would drain back into the tank ( 20 feet overhead 3/8 feed, 2 tanks piped into a y joint) . The tigerloop could get rid of the air, but this would take longer than the longest configurable TFI time. In this case the solution was adding a couple of inline check valves where the oil line exists the tanks. A workaround of not letting the system sitting idle for too long by raising the night temperature did also work.I am not 100 % sure why the cold weather came into play. Maybe, increased oil viscosity slows down the air purge from the line?
Thanks for your reply. I was just on this post a month ago because I was searching for the answer for this year's issue and humorously enough, found this post right away on Google and as I was reading it was like, "wait this sounds like me..." And sure enough was having the same symptoms on Thanksgiving.
I was thinking it was the cad sensor again, but it was within range (though better than the last time I posted 4 years ago...).
But indeed, you are correct, and this year's issue was sludge in the tank. I replaced the filter and it was much gunkier than normal, so I opened the valve with the filter off and nothing happened...
So I ended up taking off the firematic valve and on the advice of the hardware store, added a ball valve in front of it. Fortunately, once the firematic valve was off, oil came gushing out and I didn't need to replace the tank.
It was a bit of challenge to replace the valve with a full tank, but learned from my oil delivery company that Coke works great as a cleaner and was able to save all of my clothes by soaking in Coke before washing (I previously washed them a couple times in hot water to no avail).
The nozzle was also clogged, so replaced that and bought a new filter and case and I'm back in business.
The downside was my oil repair guy never returned my "emergency" call at midnight the night after Thanksgiving.…
Homeowner
Hard to find a good burner guy in my area. I have a 4 year old EK resolute boiler, with the Carlin x Pro EZ burner, and the guys who installed it apparently work with a 10x markup on the material cost. They are happy to replace one part of a time, and conclude "that was not it". I would not even mind (much) paying through the nose, if they could fix a problem in one or 2 shots.
BTW did you guys know that B20 is quite common now in New England. Not that anybody will bother to tell us. This has some implications on which Tigerloop model you can use. The very common see-through version is only "recommended" Up to B5. Not sure what happens if people use this with B20 which I am sure many do.
Call me crazy, I observe something interesting while watching the Ohm values the CAD sensor puts out. The 70200 controller has a mode where it displays this. I observe the following: As the burner warms up, the ohm value goes down.
Also, I observed the ohms while a tech was messing with the air gate, not having a combustion analyzer on him: More air, higher ohm values. I am thinking, that letting more (to much) air in, cools the burn chamber, resulting in some unburnt fuel and soot problems. My initial thought was that you could not go wrong with having too much air, and was surprised that the tech was setting an apparently low air gate open value , like 5%. The Carlin install manual says set it to 45% as a rule of thumb for a 0.75 gph nozzle.
I am aware, and agree.
Still, I like to have some theory of operations… I think CAD cells are sensitive to infrared, so the readings you get out of them are to an extent, heat readings. For example: I observe a tech saying after a cleaning "I like to start out with a <400 ohm reading when there is flame". So when I see a 1200 ohm reading, that does not necessarily mean a dirty cell, it could be just a cold chamber / too much air. After a 5 minute burn, we may see a 600 ohm reading for flame, and 30,000 ohm reading when no flame. A hot chamber. Useful to understand, no?
Combustion analyzer sensors go out of calibration/warranty every 1-2 years, so any sanity check is useful. I have seen techs scratching their head saying "these readings can't be right..", and just set the air gate to the recorded value set "at last service".
Some additional info about my Carlin Lockouts:
It was actually Carlin tech support who proposed the "slow air leak in the supply line" theory. The guy asked me if I had a check valve close to the tanks, and said "Aha! The oil drains back into the tank!".Now that think about it, there is one thing I cannot explain: How is the burner starting up from "idle" different from a red button restart"? If 20 feet of air in an 3/8 " line is too much for the Tigerloop to get rid of inside 45 seconds, why does it manage to start up from that condition when I press the reset button? It goes through exactly the same steps on reset as it does on a starting up from "idle"… Unless I am missing something.
Also: If I had an air leak somewhere, would I not have an oil leak there as well?
I adjusted the thermostat so that I do not let the house to cool off at night (up form 61F to 67F) and did not have any lockouts for a week. Prior to that I would get 1-3 lockouts per day.
After a week, tried 65F at night, and started having some lockouts. At this point I added a couple of check valves at the points where the line comes out of the tanks. Restarted and had one lockout a few hours later, but running fine after that for the 2nd day now. I have to wait longer to see if the check valves did the trick.
One more data point: I waited for a lockout to occur before I opened up the overhead lines' flare connections at the tanks to add the check valves. There was indeed no oil to speak of in the lines, as I expected.
The 70200 has an extended "prime" cycle which it may be using on a reset after "no flame" failure.
Strictly speaking, the cad cell is sensitive to visible light, biased to the infrared. It is not a thermal sensor — the IR it is looking at is well above thermal IR ranges.
The 70200 indeed has a distinct priming function, which can be invoked with a long (10+sec) button press.
When doing a simple reset, that is not activated. As per what is shown on the lcd screen, it goes through the same exact startup steps for the same lengths of time as when it starts up from idle. Pre-purge, TFI, flame stabilize, and finally burner running.
I have recently had some work done on my EK Resolute RT, when an EK rep. came on-site to supervise the upgrade of my air inducer. The EK rep dialed in the air gate settings, and pointed out, that on the Resolute there are 2 ports for flame checks. The port on the left is only supposed to be used for smoke check, and the one on the right for combustion analysis. My service techs were using the wrong port. Consequently my air gate was set way too low (2-4) for the past 3.5 years.
When the EK rep dialed in the air gate, using the correct port, the air gate ended up set to 45. So all this time my system was running lean, with poor flame quality.0 -
My "no flame" problem turned out to be an air leak at the flex tie-in lines between the tigerloop and the burner. Tightening the nuts at the tigerloop seems to have taken care of the problem.
Also on the Carlin Xpro EZ, TFI == 30 seconds works better than the default 15 secs. The same tech said setting the TFI to a too long value will lead to premature ignitor wear, although the Carlin ignitors are continuous duty rated.0 -
Is it a delevan nozzle? I have been doing oil burner service for nearly 30 years and have never seen so many problems with the nozzles. I have talked with other techs and counter men asking about any issues, and yes there are problems. Things are so bad, I hang on to the old nozzle and put replace it with the "new" one, when things go bad. Nothing is as bad when the customer says "You were just here, and was working fine before you came." I have spoke with the beckett rep. at trade shows (beckett bought delevan), he asks me "Well was it working when you left?" I reply "Yes", he replys "Must be something else". I have a collection of nozzles that I bringing to the Eastern Energy Expo and give to Delevan in May.
I think I've had one bad Delavan nozzle in the past 4 or 5 years.
Sounds more like a fuel quality issue.
Yes it is a Delavan .75 60A. I think I can exonerate the nozzle since it has been replaced back in September, and again a couple of weeks later. The burner tech suspected it after they did the yearly service, and was having lockouts When called back out, he did another cleaning and replaced the nozzle a second time, saying that these nozzles are made in China and they are sometimes having problems with them. Looking at Delavan's site, it says they make these in Ireland.
The nozzle replacement did not make any difference. The only thing that made a difference is tightening the nuts on the tigerloop flex hoses. It is a solution that gives me a couple of weeks of "no lockouts".
Because I had some weeks of trouble free operation, I am tempted to think it is not a fuel issue. The fuel in the tank is the same, did not have a fill-up all this time. I have 2 new Roth tanks , 800 gallons total,so I only buy fuel once a year.In the past 3 days, I started getting "No flame, chk ign" lockouts. The "chk ign" is new on the last 5 errors. In the past 3 months, I had probably 55+ "No flame" lockouts, never seen the "chk ign" before now.
I happen to have a brand new Carlin Pro X 45000 on hand, will replace it later today and see what happens.
Easy enough to do. If nothing else, it is a datapoint to whether I really have an ignitor problem or not.0 -
Completed the ignitor replacement, with the same Pro X 45000 (except brand new). Mostly works, but still does an occasional "No flame, chk ign".
I have put some conductive dielectric grease on the contacts, (Deoxit) . I figured it would protect the contacts from corrosion… Could this actually cause a problem, and a "low amps" flag on a brand new ignitor? I dont see how that could hurt, but will wipe it off tomorrow.
I noticed that whoever installed my system routed a couple of wires over the sharp edge of the wire box under the carlin 70200 controller. The wire did not look damaged, but seriously? All the wires into the box are supposed to be routed through the left mounting bolt hole, which is otherwise unused in this configuration.
They were thermostat wires, which I do not have trouble with.
Have you checked your electrodes to make sure they are in good condition and adjusted correctly?
Possible intermittently failing of ignition output from primary control. Easy to test. Connect hot ignitor lead to orange output lead from primary along with the motor. Viola! Constant ignition. If problem disappears replace primary.
@SuperTech, The burner was serviced in September by a local EK dealer, and they declared it OK. I have not touched it. There were a few 1-2 week periods between then and now, when the burner was working without any trouble.
@Techforlife:
Not sure which leads you are talking about, one of the low voltage terminals In front of the 70200?Or one of the spade push on terminals on the underside of the controller? The 2 outermost of these are connected to the 4500.
I never considered that the controller may cause a "chk ign" error. I have a spare brand new 70200 controller, with the latest firmware, I can swap it and see what happens. Because the problem is intermittent, it is hard to come up with a test that would nail this in one.
If you have a new 70200, do the swap. At least we can perform some process of elimination. Wiring should be obvious with color coding. FYI, I was referring to the spade terminals that supply line (115) volts to the components.
Took apart all the wire connections from the 70200 to the ignitor, and wiped off all the Deoxit dielectric grease. Works a lot better, no more ignitor errors for a couple of days. Deoxit advertises this grease as "conductive" with copper particles infused, but apparently, for this application, it impedes current flow enough to cause an intermittent "low amps" problem. Surprised the heck out of me, lesson learned.
(I use Deoxit on automotive electronic contacts all the time to prevent corrosion).
I cleaned of the deoxit grease with brake cleaner, and rubbed the contacts down with contact cleaner. I also tightened the wire connectors that slide onto the terminals. After this, no more "chk ign". Lockouts still occur after the flex hose nuts come lose at the tigerloop, but I do not see the extra "chk ign" message. I think what is happening here: normally, the controller does not check the ignitor voltage, only does when there is a "no flame" condition. So the primary error is the no flame, which occurs because loss of prime. When that happens, the ignitor voltage is then checked and the "chk ign" is set. So, the ignitor voltage may be marginal, but you may never see an error flagged untill there is a no flame condition, possibly for some other reason.0 -
I guess we have diverged a bit form the OP-s topic. @jondaley, what type of Primary controller you have ? Is it the Carlin 70200? If not, it is worth it to swap the current one out for that.
The 70200 has a number of diagnostic features, e.g. it will give you an optional continuous ohm reading on the CAD, and logs up to 32 errors (including restarts) with additional error indicators. When all the error logging "slots" are full , it will overwrite the old errors, starting with error 1.
Latest "twist" in the saga: looks like when the system was installed, the flex line was twisted. Because the non-turning nut end was tightened last, on the tigerloop side. This left tension in the flex lines, which, combined with vibration, un-twists the nuts there, leading to the air leak.
- 119 Chimneys & Flues
- 165 Indoor-Air Quality
- 76 Pipe Deterioration
- 15.6K Strictly Steam