Aqua Balance 155 combi
denis040
Member Posts: 7
Hello,
My brother and I installed the Aqua Balance 155 combination boiler. It’s working great except I keep getting some water out of pressure relief valve. My pressure reducing valve is set for 15 but the pressure gauge on the system reads over 20. Could this be as simple as a bad pressure reducing valve?
did you set the expansion tank up to 15~16?
is it properly located? pumping away from it ?
Pictures?known to beat dead horses0 -
Thanks for the reply. Here is the picture.
one more picture showing your circulator(s) also,
was the tank pressure adjusted up ?known to beat dead horses0 -
When does it release ?
Tank pressure is for 15
Releases a bit when it’s over 30. Just confused why it’s even getting up that high
what is the temperature at 30# ?
Temperature is 1400
you should request @Erin Holohan Haskell combine these 2 threads,
my temp question doesn't matter,
the possible domestic tank does,known to beat dead horses0 -
Domestic is set for 118. Thank you for your help!0
I combined the two threads here. Thanks!neilc said:you should request @Erin Holohan Haskell combine these 2 threads,
President
HeatingHelp.com0 -
Yeah, @Big Ed_4 is right. Try reducing the pressure and shut down the ball valve before the pressure reducing valve and see if it makes a difference.
That definitely looks like a potable water expansion tank, which is the wrong tank for the boiler. I'd replace the tank, make sure the air pressure is set before you install it on the boiler and relocate the reducing valve so its between the tank and the air separator.0 -
You guys are best! Thanks so much. Hope you all had a wonderful thanksgiving0