Oversized radiator
fxrgrunt
Member Posts: 157
This bad boy is way oversized for the room it is in. Primarily because they built it for a larger room and at some point someone walled off a walk in closed taking about 100 sqft away from the room. I even tried shutting the vent all the way and this thing is still piping. What are my options to get it where I need to be? Keep in mind I haven't built the top of the cover yet but it will still not be enough being this thing is ridiculous. I'm talking 82 degrees in that room right now.
Throw some insulation over it inside the box
I shut the hoffman 1a completely and it's still getting extreme heat. I dont want it all the way off because then there wouldnt be any heat in the room.EBEBRATT-Ed said:Block the airflow0 -
President
HeatingHelp.com1 -
I will have to try that with the vent. The pressuretrol is set at .5 with 1 cut in. Rad is 4th radiator on 66ft main line about halfway down the main. It is a 2nd floor radiator as well.neilc said:flip the vent upside down just to see if you can stop the steam from getting in that rad, what pressure are you running at? and is rad close to boiler? a higher boiler pressure could be forcing steam into the larger area of the large rad, and setting up a vacuum cycle (?)0 -
Insulating within the cover is an easy low cost way to stop a hot radiator from heating the room and with the cover you are building it will be hidden, so thats a solution. But I find it hard to believe you cannot slow or stop the radiator from fully heating by closing the vent. It sounds like your steam system is running longer than it should. Perhaps the vents on the other radiators need to be opened more to allow the other radiators to heat quicker and satisfy the thermostat sooner. If that's the case, it would be a better solution.1
@fxrgrunt
When I said block the airflow I wasn't talking about the vent.
Block the airflow coming into the bottom and front of the radiator. Block half of it off. Too cold take some off. Still too much heat block some more1 -
Got ya. I will try this! And take into account what everyone else has suggestedEBEBRATT-Ed said:@fxrgrunt When I said block the airflow I wasn't talking about the vent. Block the airflow coming into the bottom and front of the radiator. Block half of it off. Too cold take some off. Still too much heat block some more0
- 120 Geothermal