How cold for above-ground LP tanks to have issues?
sunlight35
sunlight35 Member Posts: 35
What's the typical low temperature for above-ground propane tanks not able to provide sufficient gas pressure needed for boiler? My boiler requires a minimum pressure of 10 w.c.
  • GroundUp
    GroundUp Member Posts: 2,387
    As long as you keep it above 5% full, you'll never see weather cold enough to cause problems.
    EBEBRATT-Ed Member Posts: 18,319
    What @GroundUp said
    Above ground tanks are quite common. Not an issue
  • Oliveone
    Oliveone Member Posts: 7
    That funny :)
  • Solid_Fuel_Man
    Solid_Fuel_Man Member Posts: 2,644
    There is a formula for wetted surface of the tank (how full it is and type of tank), outside temperature, and btu/hr draw of vapor.
    Technically, at -45F the liquid will not vaporize.
  • Zman
    Zman Member Posts: 7,611
    Above ground tanks usually don't have issues. I do have a client with a 4,000 gallon tank and over 6,000,000 attached load in climate zone 7. They have issues and need to run a vaporizer to make it work.
    How big is the tank and boiler?
    Albert Einstein
    Yes the tank has to have enough surface area to be able to absorb heat to vaporize the liquid based on the connected load
  • Robert_25
    Robert_25 Member Posts: 554
    It depends on your btu load, and how full the propane tank is.  Google "propane tank vaporization chart" and you will see what I mean.
    At -45F you could store the propane in a 5 gallon pail.
  • sunlight35
    Thanks, I think I was mistaken w.c. for psi.
    hot_rod Member Posts: 25,437
    I was on the maintenance team at Snowbird resort when it was first built, all LP boilers. The vaporizers were in a concrete vault in an avalanche path. Talk about a scary appliance to work on.
    They finally ran a NG line up the canyon.