Skimming
Now my question is where on this boiler should I be installing the tap for skimming. On the side that the header is on there is already a T with a cap that I could pipe off of but not sure if that is ideal. On the side that the gauge is on there is a 2 1/4 inch tap as well that I could run a nipple with valve out of. I've also read you could pipe a T off the pressure release but mine is on top and I heard it should be on the side if you do this. Also, should I go with 1"insulation or 1.5"? Any info would be much appreciated. See attached.
Just remove the plug that is in the tee ,there’s your skim tapping. I would put a 21/2 x 1 1/2 bushing and then add a nipple and elbow and possibly a piece of pipe for a drop . From the looks of the sight glass the boiler is dirty looking like mostly mud . I would first wand the boiler from the top through the plug in the tee it the only upside to side outlet boilers in my opinion and then fill and skim . Open the lower drain valve and empty the boiler and insert a wanding tool and flush water thru each section spray and loosing mud and debrie from the water side of each section finally when you see that it’s all clear and no mud or dirty water is draining out ,close the drain use the boiler feed valve and fill the boiler to normal water level ,turn on the boiler and let fire till the water is about to steam and shut off the burner and fill w water till it comes out the skim tapping trickle water out the skim tapping until it runs clear . Drain to proper level and install the plug again and your clean . From the looks of your pictures it hard to tell if your Hartford loop is correct . As for insulation use a mim 1 inch wall thicker is better but make sure u have the clearance . Near boiler piping doesn’t look to great either but that’s another topic but could be your reason for surging . Usually we use both tapping on that style boiler they tend to perform better w less surging . You can go online and download the installation and operation manual it will give a diagram and pipe dimension for the proper piping of your boiler , usually there riser and header dimension are on the small side and most pro s always tend to upsize them for dryer steam and better system overall performance . Peace and good luck clammy
R.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating2 -
On a quick note they should also be cleaning the pigtail ,sight glass and removing and cleaning your low water cut off probe aside from testing them for proper operation . Aside from the water side of things they should be giving some attention to the gas and flue side of things also but sometimes a lot of that stuff is not included or they don’t do that type of service . Peace and good lucks clammy
NJ Master HVAC Lic.
Mahwah, NJ
clammy said:Just remove the plug that is in the tee ,there’s your skim tapping. I would put a 21/2 x 1 1/2 bushing and then add a nipple and elbow and possibly a piece of pipe for a drop . From the looks of the sight glass the boiler is dirty looking like mostly mud . I would first wand the boiler from the top through the plug in the tee it the only upside to side outlet boilers in my opinion and then fill and skim . Open the lower drain valve and empty the boiler and insert a wanding tool and flush water thru each section spray and loosing mud and debrie from the water side of each section finally when you see that it’s all clear and no mud or dirty water is draining out ,close the drain use the boiler feed valve and fill the boiler to normal water level ,turn on the boiler and let fire till the water is about to steam and shut off the burner and fill w water till it comes out the skim tapping trickle water out the skim tapping until it runs clear . Drain to proper level and install the plug again and your clean . From the looks of your pictures it hard to tell if your Hartford loop is correct . As for insulation use a mim 1 inch wall thicker is better but make sure u have the clearance . Near boiler piping doesn’t look to great either but that’s another topic but could be your reason for surging . Usually we use both tapping on that style boiler they tend to perform better w less surging . You can go online and download the installation and operation manual it will give a diagram and pipe dimension for the proper piping of your boiler , usually there riser and header dimension are on the small side and most pro s always tend to upsize them for dryer steam and better system overall performance . Peace and good luck clammy
Your tee with the plug is only 2", there is a reducer bushing installed into the 2 1/2 port. This should have been 2 1/2" out and up and for the horizontal header before it dropped down as the equalizer. This may contribute to wet steam also.
Cleaning may solve your problems....it is a fairly major job to repipe and I would certainly try the cleaning first.
But as Clammy said wand washing and then skimming will go a long way in improving the steam.
I would reduce the 2" to 1 1/4" skim port.
Some of these boilers have reduced openings between sections and if you do not reduce you only skim the section closest to the port. You want to float the oils above all the sections inside and reducing the outlet will do that.
There are U-tube video's for wand washing your boiler.
Also here on the wall is a posting "Losing 10 gallons a Month"
It has info on easy skimming, I have tried this technique and it works well.1 -
I've seen worse!
ethicalpaul said:I've seen worse!
I agree with @ethicalpaul
Piping isn't text book but it's not terrible. A good cleaning and skimming you will probably be fine1 -
Insulating the supply pipes may also reduce the wetness of the steam.—NBC0
As other filled in the blanks ,the near boiler piping is off and so is the Hartford loop it should be a close or shoulder nipple and a elbow facing down ,the way it is it probably makes some noise . As for pricing we don’t discuss on line . The one steam main should not have that horizontal pipe and then 2 elbows it should have been straight vertical into the existing main or add a small drip . The boilers looks to be about 5 years old it may pays to repiped it properly being it has a good 15 year life span left and then u will get 15 years of dry steam and proper operation . Wet steam does no good in all aspects it does not put the heat where it’s needed in a timely manner ,increases condensate in mains and leads to pipe grooving and leaking . While your at it get mains vents either cut in or replaced and new quality radiator vents . Wet steam sucks and makes balancing difficult at best .if your in for the long haul get it fix and working as it should . Peace and good luck clammy
NJ Master HVAC Lic.
Mahwah, NJ
Closer look this is a counter flow system and yes it’s piped wrong hence the banging . You need drips for each main and forget the main vents ,this type of system really needs dry steam other wise they work terrible ,get it repiped and new rad vents then look into insulating that piping then you ll be in good shape , both supply tapping should have been used and and it should be 2 2/12 risers into a 3 inch header w 2 inch over head drop supplies and a drip for each main ,then ur in good shape clammy
NJ Master HVAC Lic.
Mahwah, NJ
clammy said:Closer look this is a counter flow system and yes it’s piped wrong hence the banging . You need drips for each main and forget the main vents ,this type of system really needs dry steam other wise they work terrible ,get it repiped and new rad vents then look into insulating that piping then you ll be in good shape , both supply tapping should have been used and and it should be 2 2/12 risers into a 3 inch header w 2 inch over head drop supplies and a drip for each main ,then ur in good shape clammy
Damian0 -
And just to compound your life more, is that a garage door in the back ground that would allow a vehicle to be parked inside?
Also in one picture there looked to be 3 fuel jugs sitting across from the boiler.
There is a graphic warning label on the water heater showing gas fumes traveling across the floor to find the flame of appliances.
Just pointing this out for you information.
Most codes require gas burning appliances to be installed 18" above the floor of a garage for this reason.
We are not the code police here but just want you to be aware of potential issues.0 -
JUGHNE said:And just to compound your life more, is that a garage door in the back ground that would allow a vehicle to be parked inside? Also in one picture there looked to be 3 fuel jugs sitting across from the boiler. There is a graphic warning label on the water heater showing gas fumes traveling across the floor to find the flame of appliances. Just pointing this out for you information. Most codes require gas burning appliances to be installed 18" above the floor of a garage for this reason. We are not the code police here but just want you to be aware of potential issues.0
The intent of this 18" is to place a source of ignition above the floor in the event of a gas leak in a vehicle or even a lawnmower, snow blower etc.
Even the fumes from gas jugs that might outgas as the lids are seldom vapor tight.0 -
JUGHNE said:The intent of this 18" is to place a source of ignition above the floor in the event of a gas leak in a vehicle or even a lawnmower, snow blower etc. Even the fumes from gas jugs that might outgas as the lids are seldom vapor tight.0
JUGHNE said:Just removing any fuel containers from the room will probably suffice now that you are aware of the potential. Raising the boiler also raises the water line which can have bad consequences.1
LOL, I'm not sure I've even seen a steam boiler much less worked on one, but I've been gorging myself on the knowledge of this group recently with all the recent posts on steam heat. I also think they're fascinating.fxrgrunt said:Steam systems are extremely fascinating once you start reading into it and learning.
Now that I see that garage door there it would be wise to insulate the pipe and in case I think I would go w 1 1/2 wall thickness ,you have a counter flow and not insulated that doesn’t help quite it down . As for it kinda being in a garage and the raising the boiler and hot water heater to meet codes may not work to well in relationship to ceiling height ,boiler piping and such but you could frame up a mechanical room and add a fan in a can for combustion air and then it s not a issue . Peace and good luck clammy
NJ Master HVAC Lic.
Mahwah, NJ
It has been said that abestoes abatement people can mess up your pipe hangers.
Before reinsulating you want to check the slope of the steam mains.
If it is counterflow as Clammy says then the pipes should slope so as to drain back to the boiler.
The slope needs to be consistant with no belly sags.
Extra hangers are always a good idea.1 -
clammy said:Now that I see that garage door there it would be wise to insulate the pipe and in case I think I would go w 1 1/2 wall thickness ,you have a counter flow and not insulated that doesn’t help quite it down . As for it kinda being in a garage and the raising the boiler and hot water heater to meet codes may not work to well in relationship to ceiling height ,boiler piping and such but you could frame up a mechanical room and add a fan in a can for combustion air and then it s not a issue . Peace and good luck clammy0
The slope of the steam mains....counter flow is having the steam traveling in one direction away from the boiler with the condensate returning in the same pipe back towards the boiler.
The low point of the steam main is at the boiler so the condensate water will flow by gravity back to the boiler.
Mostly we see parallel flow, steam going out towards the rads and condensate flowing in the same direction as steam.
The high point of the steam is at the boiler and at the end of the steam main is a return pipe to return the water. The return would be lower than the steam main and slope down towards the boiler to drain the water back. Unless you have a "wet" return which is below the water line of the boiler....it is always full of water....your system dumps water in one end and it comes out the other....the pipe is always full.
By using a level you can determine which way the condensate will flow in the steam main.
Some mains may have a combination of both, perhaps a short counterflow pipe for starting and then change slope for parallel flow after that.
Or one main could be parallel and the other counterflow.0
- 87K THE MAIN WALL
- 112 Chimneys & Flues
- 106 Geothermal
- 979 Plumbing
- 387 Solar