Connecting a C-Wire, Need advise

Heating_Noob
Member Posts: 2
I have heat only 2 zone force hot water system. L8148E Aqua stat controller. 40 VA external transformer. On the bottom of transformer, it has letters R (Load), and C. Does the C mean common??
The following is the wiring diagram but I'll try my best to describe it as well.
Stat-A "Rh" --> Trans "R"
Stat-B "Rh" --> Trans "R"
Stat-A "W1" --> TacoA "#1"
Stat-B "W1" --> TacoB "#1"
Stat-A "C" --> not connected
Stat-B "C" --> not connected
L8148E "T" --> TacoA "#2" --> TacoB "#2" --> Trans "C"
L8148E "Tv" --> TacoA "#3" --> TacoB "#3"
L8148E "w" and "z" are connected from factory with jumper
Should I connect Stat-A "C" & Stat-B "C" to Trans "C" or L8148E "z"
I used "A" for zone1 and "B" for zone2 in description.
The following is the wiring diagram but I'll try my best to describe it as well.
Stat-A "Rh" --> Trans "R"
Stat-B "Rh" --> Trans "R"
Stat-A "W1" --> TacoA "#1"
Stat-B "W1" --> TacoB "#1"
Stat-A "C" --> not connected
Stat-B "C" --> not connected
L8148E "T" --> TacoA "#2" --> TacoB "#2" --> Trans "C"
L8148E "Tv" --> TacoA "#3" --> TacoB "#3"
L8148E "w" and "z" are connected from factory with jumper
Should I connect Stat-A "C" & Stat-B "C" to Trans "C" or L8148E "z"
I used "A" for zone1 and "B" for zone2 in description.

0
Comments
-
You are going to want to connect to the C on the transformer not the aquastat."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Thank you very much. I connected to Trans "C" and it works great. The Voltage is pretty constant right now. I had 2 Nest both installed at same time and less than 1 year old. 1 die and 2nd dropping WiFi a lot. Hope this will fix the problem.0
-
-
I am surprised as well, especially with a taco 3 wire valve in the mix. The OP posted a great diagram. That sure makes it easy.I'm impressed! That question-answer-realization process usually takes much longer.
"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0
Categories
- 117.3K All Categories
- 82.7K THE MAIN WALL
- 2.7K A-C, Heat Pumps & Refrigeration
- 43 Biomass
- 400 Carbon Monoxide Awareness
- 7 Chimneys & Flues
- 1.6K Domestic Hot Water
- 4.3K Gas Heating
- 106 Geothermal
- 148 Indoor-Air Quality
- 2.7K Oil Heating
- 45 Pipe Deterioration
- 674 Plumbing
- 4.8K Radiant Heating
- 353 Solar
- 13.2K Strictly Steam
- 2.9K Thermostats and Controls
- 47 Water Quality
- 31 Industry Classes
- 64 Job Opportunities
- 11 Recall Announcements