Bypass valve
Snowmelt
Snowmelt Member Posts: 1,457
I have a 300,000 water boiler, it’s like a 400 linnier feet of piping it’s not a high it’s a standard boiler in the chimney, I want to put a bypass , the question is does Caleffi or any other have something like a three way valve so I can assure nothing under 140 degree goes back to the boiler when it’s heated.
  • Dave H_2
    Dave H_2 Member Posts: 621
    Danfoss ESBE makes a thermic bypass valve, maintains that 140F return
    https://www.danfoss.com/en-us/products/valves/dhs/thermostatic-valves/esbe-vtc511-thermic-valve/
    Dave H.
    Dave Holdorf
    Taco, Inc
  • Snowmelt
    Thanks dave, also other day on a Facebook page good job chiming in on that bad vs pump........
    Dave H_2
  • Bill_17
    Bill_17 Member Posts: 73
    ESBE makes two different actuators with built in temperature setpoint controls (CRA112 and CRA122) that could be used along with a 3 way (motorized) valve to manage the return water temperature to a boiler on a large system. They run on 24V power.
    hot_rod Member Posts: 26,631
    edited October 2020
    Here is some info on the Caleffi 280. Available up ti 14Cv, 1-1/4"
    A 3 way thermostatic is going to be the best and least expensive option, probably.
    300K will probably require a 1-12 or larger valve.
    https://www.caleffi.com/sites/default/files/file/01223_17_na.pdf
  • HomerJSmith
    HomerJSmith Member Posts: 2,712
    edited October 2020
    I have used a Taco I-Series setpoint mixing valve with a temp sensor as a bypass valve, works great, but more expensive.
    Is this a sno melt application where the water come back super cold? A flue condensate problem?
  • Snowmelt
    No just a school with a long run I feel more comfortable if a bypass was in there so the return water didn’t take such a long time to heat up
