Wirsbo Manifold Adjustments
rileyrealestate
Member Posts: 2
Hi, Looking for some help. Purchased a 20-year house in MN with Wirsbo floor heat in the basement. It has 8 zones. Looking to adjust the manifold to increase heat in some rooms and decrease in others. I read that the initial setting (mid-point) is a dime above the brass collar. Is it correct that screwing the black disk on top of the manifold down all the way will open the zone up completely and conversely, screwing the black disk on the top of the manifold up all the way will close the zone completely? This seems backwards to me, plus, my threading is about 1/2 inch, so a dime does not appear to be midway. Can anyone offer me some advice. Thanks in advance!
Yes , I would first make sure the manifold is piped correctly . Most are installed incorrectly . It should be piped reverse return , Meaning ...The first loop out should be the last to return . Post photos of manifolds and label each loop . Piping it incorrectly is a Normal mistake
There is absolutely zero reason for reverse return piping with radiant manifolds. None whatsoever. If there were even the slightest bit of pressure drop (there never is), that's why we have balancing valves. Reverse return is a complete farce and waste of time in this regard.
To the OP, yes you are correct with how the loops adjust. Do your manifolds have the glass flowmeter globes on top? Some do and some don't. Without flowmeters, it's really just a crapshoot unless you know the exact length of each loop. You can start by cranking in the valves on the zones you want cooler by a turn or so, and waiting a couple days to see how it responds. It may take weeks to get it dialed in, but there's not much other choice that I'm aware of without flowmeters1 -
When we talk reverse return on radiant manifolds, it is merely staggering the loop connections. So the first loop fed, is the last returned. Really over a very short manifold trunk dimension it is probably not a huge deal.
Ideally a load calculation and radiant design would indicate where to set each balance valve.
Or as you suggest, adjust to your needs or liking. That is one of the beauties of hydronics, very adjustable.Bob "hot rod" Rohr
Living the hydronic dream1 -
To the responders, thank you. Just 2 basic questions. The black top disk (no glass flowmeter globe). Is it correct that if I turn it clockwise or crank it down to the brass collar, it opens it up completely? Conversely, when I turn it counter-clockwise or crank it up from the brass collar, it closes it completely? Secondly, I read that a midpoint is 1 dime width above the brass collar, is that correct? This is a 21-year old Wirsbo system with 8 zones (16 hoses), heating about 2,500 sq. ft. in the walkout basement level. The central heating has supplemental vents in the ceilings. Thanks again.0
I have always questioned the notion of reverse return -- has there ever been any real world study of this ? My memory of fluids class (not prefect) ... seems to say that with proper circulator ... flow /head -- this is not happening.
conceptually it is pretty simple, resistance in each piping path would match.
In reality the calculations look like this.
The perfect RR would have then pipe sized to the gpm each section sees. So pipe size reduces as loads are taken off, reversed on the return.Bob "hot rod" Rohr
Living the hydronic dream0
- 121 Chimneys & Flues
- 15.8K Strictly Steam