Yes , I would first make sure the manifold is piped correctly . Most are installed incorrectly . It should be piped reverse return , Meaning ...The first loop out should be the last to return . Post photos of manifolds and label each loop . Piping it incorrectly is a Normal mistake
There was an error rendering this rich post.
1 -
There is absolutely zero reason for reverse return piping with radiant manifolds. None whatsoever. If there were even the slightest bit of pressure drop (there never is), that's why we have balancing valves. Reverse return is a complete farce and waste of time in this regard.
To the OP, yes you are correct with how the loops adjust. Do your manifolds have the glass flowmeter globes on top? Some do and some don't. Without flowmeters, it's really just a crapshoot unless you know the exact length of each loop. You can start by cranking in the valves on the zones you want cooler by a turn or so, and waiting a couple days to see how it responds. It may take weeks to get it dialed in, but there's not much other choice that I'm aware of without flowmeters1 -
When we talk reverse return on radiant manifolds, it is merely staggering the loop connections. So the first loop fed, is the last returned. Really over a very short manifold trunk dimension it is probably not a huge deal.
Ideally a load calculation and radiant design would indicate where to set each balance valve.
Or as you suggest, adjust to your needs or liking. That is one of the beauties of hydronics, very adjustable.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
To the responders, thank you. Just 2 basic questions. The black top disk (no glass flowmeter globe). Is it correct that if I turn it clockwise or crank it down to the brass collar, it opens it up completely? Conversely, when I turn it counter-clockwise or crank it up from the brass collar, it closes it completely? Secondly, I read that a midpoint is 1 dime width above the brass collar, is that correct? This is a 21-year old Wirsbo system with 8 zones (16 hoses), heating about 2,500 sq. ft. in the walkout basement level. The central heating has supplemental vents in the ceilings. Thanks again.0
-
-
-
I have always questioned the notion of reverse return -- has there ever been any real world study of this ? My memory of fluids class (not prefect) ... seems to say that with proper circulator ... flow /head -- this is not happening.
0 -
conceptually it is pretty simple, resistance in each piping path would match.
In reality the calculations look like this.
The perfect RR would have then pipe sized to the gpm each section sees. So pipe size reduces as loads are taken off, reversed on the return.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Good morning .. anyone around to review my dilemma ? My Wirsbo system was installed 20+ years ago .. 5 loops .. 2 thermostats ..
original design =
bathroom thermostat controlled 1 loop .. #4 loop (bathroom) 119'
living room thermostat controlled 4 loops #1 loop (bedroom) 150'
#2 loop (entry) 167'
#3 loop (living room) 228'
#5 loop (kitchen) 196'
I rewired the system myself ..
I wired the 3 shorter loops ..
#4 119' eastside
#1 150' northside
#2 167' northside
to the bathroom thermostat ..
I wired the 2 longer loops ..
#3 228' southside
#5 196' southside
to the livingroom thermostat
I have proved it
the 2 longer loops DO NOT completely exchange the cool water for hot ..
the 3 shorter loops DO completely exchange cool water for hot ..
(it takes only nine minutes from raising the thermostat in the bathroom to feel the hot water in the return pipe)
I am okay with the 2 longer loops exchanging the cool water for warm (not hot) in the same 9 minutes ..
MY DILEMMA
are the loops not completely exchanging cool water for hot causing my dilema?
it is causing the wicked static pulling dust like bunnies to the floor and everywhere really ..
I am wondering why the static problem NOW?
did it start when I rewired the loops
without adjusting the loop pressure?
any suggestions?
thank you ..
0 -
Did you drain water out to make the changes? If so it could be air locked.
Or mis wired?
Static is often due to low humidity in the space.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Thank You for your prompt response. .
- I did not drain the system. ..
I do not know how to do that ..
Would an air lock create static?
I think i would have to call someone to flush the system ..
2. i think the wiring is right ..
I see the WIRSBO VALVE cylinder rise/fall as i increase/decrease the temp on the thermostats ..
on the 3 short loops when I turn the temp up/down on the bathroom thermostat..
on the 2 long loops when I turn up/down on the livingroom thermostat ..
3. my building is small. 726' ... the 6" concrete slab is exposed .. yeah .. yes low humidity .. I use throw rugs .. I also arranged some cut wooden flooring boards into rug size wooden mats. .. I place rugs on top of them ..
I am trying to understand when/why the static started. .. 3 or4 years ago ..
For many years the floors stayed so clean .. I rarely had to sweep or mop the concrete floor .. never saw any lint like bundles .. not like now … the bundles are bigger almost daily .. I first noticed the excess lint in the dryer .. almost always pinkish .. 8 or 10 times bigger than a cotton ball .. with every dryer load ..
Would painting the floor with anti-static paint help? .. Would that restore the floor like before the static started ?
Thank You for your expertise...
again Thank You again
camp
I am hoping to rule out the floor ..
0
Categories
- All Categories
- 87.5K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 430 Carbon Monoxide Awareness
- 122 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.9K Gas Heating
- 118 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 395 Solar
- 15.9K Strictly Steam
- 3.5K Thermostats and Controls
- 57 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements