How to test a Radiator Steam Trap
How do you know when a steam is bad?
    Jamie Hall Posts: 27,916
    It will either fail open or closed. If it fails closed, the radiator won't heat at all, or very very poorly (and may even fill with water!). If it fails open, it will allow steam to pass once the radiator is more or less full -- and the outlet, measured a few inches beyond the trap -- will be as hot as the trap inlet.
  • JohnNY
    JohnNY Posts: 3,416
    When a radiator trap fails open, that radiator tends to get very hot while it causes others, usually nearby, to not get hot.
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
  • Dairon421
    Dairon421 Posts: 81
    edited October 2020
    Thanks guys. So now I understand that when a steam trap fail open it often gets to hot and cause other radiators not to heat because there will be steam in the return. When a steam trap fail close the radiator will not heat but the others will heat because the steam not entering the returns. Am I correct?
    JohnNY
    Got it
    Dairon421