Boiler size for Wirsbo garage heat 1000sq ft
amons
Member Posts: 3
Hi.
I am looking for advise on sizing a boiler for wirsbo garage heat.
1000sq ft attached garage
r-19 garage doors. 16’, 9’, 7’. All 7’ high
r-60 ceiling r-20 walls.
Well sealed.
Minneapolis MN
this is our only garage so the doors will open a few times per day.
looking to heat air temp to 50-55 degrees
there are 5 loops about 160 ft each 1/2” pex.
boiler will only be used for the floor heat.
What variables am I missing? Google searches are putting the btu requirements all over the map.
Based on my research it looks like I should be purchasing a modulation condensing boiler. Any reason I shouldn’t?
thanks!!
thanks!!
Forgot to mention. There is 2” foam under the slab and around the entire foundation0
Probably want to run glycol in it in case it isn't heated at some point for some reason.0
I know you said the boiler will only heat the attached garage....but what heats the house now? Forced air I presume.
Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0 -
This was an addition to the existing home. We tore off the existing garage and slab. Added a mud room and reconfigured the garage and made it way larger. The home has forced air. I am sure I will want to run Pex for heat everywhere once I have warm toes in the garage but I will have to cross that bridge another day.
I will run the glycol for sure.Sadly my neighbor did something similar and had a 120btu boiler installed. I was think that
must be way too large based on what I have read.0 -
Complete stab in yue dimly lit room guess is your heatloss will be in the 15,000-20,000 btu/hr range. May even be lower. Smallest mod/con will cover the load without issue. If you do decide to heat the whole house with water someday, you will likely still have enough capacity left from this mod/con to do that as well.
Again, to make the real determination we would need to do a proper heatloss calc on the house etc.Serving Northern Maine HVAC & Controls. I burn wood, it smells good!2 -
I'm in Minneapolis (Loring Park area) every day and would be happy to perform a heat loss calc for you if you'd like, but as these fellas said, any mod/con on the market today would be plenty. I wouldn't guess that load to be over 15-20k given the info you provided. I could even set you up with a boiler, feel free to send a PM if you want to discuss options.0
Unless you want to add some snow melt too