Hydro Air short cycle?
I guess I need to balance the system. How do I do it? Restrict the flow to the hydro air loop?
Thanks
Need to know more about the controls.
Ideally, when the hydro zone calls, the control should reset the boiler to a higher temperature, like it does for DHW. So the outdoor reset is working against you.
It's not seeing hot enough supply water temp to keep the fan running.There was an error rendering this rich post.
Does it heat the space adequately? It might make more sense to slow the blower speed or run the blower off a timer from the t-stat rather than off an aqua stat if it has adequate output at the reset temp.0
The boiler is Uitca MACF-150 (combi). My understanding is: the thermostat call is connected to a TACO 4-zone zone valve controller, which then is connected to the boiler control terminals. When heat is called, the boiler starts up and the primary circulator (built-in in the boiler) starts. Then the secondary circulator starts.
The heating side set point is controlled by the outdoor sensor. I read the supply temp at ~120F. The dhw is not controlled by the outdoor sensor.
I suspect that the hydro air system has higher heat output, so that the room temp is satisfied earlier than the baseboards. Can I just partially close the valve to the hydro air loop? any down sides?STEVEusaPA said:Need to know more about the controls.
It's not seeing hot enough supply water temp to keep the fan running.0 -
Yes. It heats adequately. It satisfies the same thermostat set temp a lot quicker than the baseboard loops. Slow down the blower may be a good idea, even though I don't know how to do it. I guess I need to reduce the heat output of this loop so that it matches other loops. I am thinking about restricting the flow to that loop.mattmia2 said:
The hydro coil has a huge BTU output so some regulating of the air temp is needed. Slowing the fan, limiting the water temp in and or out.
Taco speed drive pump measuring return water is good for that.0 -
Limiting water temp is not feasible. I have one boiler, so the supply water temp is the same for all zones. I will look into slowing down the fan. Are there any disadvantages of reducing the water flow rate? I can easily do it by turning the valve. Does it hurt the secondary circulator (TACO 0015E3 3-speed)?pecmsg said:
if you reduce the water temp/flow too much without reducing the airflow, it will feel cold and drafty.0
Thanks for the advise. I am not quite comfortable of adjusting the blower by myself. Need to find the manual of the unit.Big Ed_4 said:
You would be better off controlling the air flow . Most air handlers use mutable speed blowers. . Normally Heat would be half the CFM's of AC ...
What controls the fan in heat mode? The thermostat, aquastat, relay, sequencer?0
TACO Viridian for that circuit!budalb said:Limiting water temp is not feasible. I have one boiler, so the supply water temp is the same for all zones. I will look into slowing down the fan. Are there any disadvantages of reducing the water flow rate? I can easily do it by turning the valve. Does it hurt the secondary circulator (TACO 0015E3 3-speed)?
pecmsg said:The hydro coil has a huge BTU output so some regulating of the air temp is needed. Slowing the fan, limiting the water temp in and or out.
Taco speed drive pump measuring return water is good for that.1
- 119 Chimneys & Flues
- 165 Indoor-Air Quality
- 76 Pipe Deterioration
- 15.6K Strictly Steam