Expanding Taco Relays

Options
chernomorez
chernomorez Member Posts: 2
edited September 2020 in Thermostats and Controls
So, I have a 4-zone / 4-circulator system connected to Taco SR-504-4. Now, I'm adding another zone with it's own circulator. This zone would also need to have a common wire available for the thermostat What are my options for the relay:
  • Discard SR-504-4 and get SR-506 or SR506-EXP (most expensive, but easiest to wire)
  • Buy another SR-501/502 and wire it in parallel to the SR-504 (much cheaper, but is it even possible, or I must have the -EXP's)
  • Same as above, but wire as master-slave.
  • Any other options?

Comments

  • HVACNUT
    HVACNUT Member Posts: 5,841
    Options
    What's connected between the SR504 and the aquastat? The XX dry contacts or ZR,ZC?
    If using XX, an SR501 will be fine. Unless your thinking of adding another zone down the road. 
  • Ironman
    Ironman Member Posts: 7,376
    Options
    Like this:


    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    STEVEusaPA
  • chernomorez
    chernomorez Member Posts: 2
    Options
    Thanks to all who replied. Ending up buying an open box sr506 on Ebay and selling my older sr504.