Is two automatic air vents necessary?
shredmaster
shredmaster Member Posts: 30
edited August 2020 in THE MAIN WALL
I have a Weil Mclain CGA 5 boiler, the illustration manual has two air vent 10 and 13 but i've seen some very experienced plumber only install automatic air vent on position 10 like this video. https://youtube.com/watch?v=f3JXaU3XGGg
I like to keep things simple and not install additional air vent but would like to know disadvantage not having one.
  • Ironman
    Ironman Member Posts: 7,859
    #13 is actually an MBR and is more critical than #10. If you have a bladder expansion tank (as pictured), you must have #13 to vent the system.
    Bob Boan
  • shredmaster
    thanks for quick response. the manual sounds like #13 can be optional.
    how is #13 different from #10, aren't they both just eliminating the air?
  • Ironman
    edited August 2020
    It depends on the type of expansion tank. If you have the old style compression tank, then an air separator (MBR) should never be used. Instead, a means to move air from the top of the boiler to the tank should be employed to maintain the air cushion in the tank.
    If you have a bladder tank, then an MBR must be used to remove air from the system.
    The alternative method shown in the diagram may work, but it's not as effective as using a Micro Buble Resorber. I would use it on a system with cast iron rad's where any air not removed at the boiler would automatically go to the top of he rad's and be manually bled.
    Bob Boan
    shredmasterSuperTech