Adding a 3rd call for Boiler ignition through an SR502
bhilton
Member Posts: 54
Hello,
I have an SR502 setup with zone 1 being my infloor heat (relay turns on the Grundfos for infloor heat) and zone 2 is my LifeBreath furnace that also has a Grundfos pump.
Everything is working as planned.
I've recently poured a new floor with infloor heat in my detached garage.
I have an SR501 left over that I want to use with a t-stat in the garage to engage the new Grundfos pump in the garage.
Is there a terminal on my SR502 I can use to connect a wire from the garage to simply tell the boiler to fire up?
Pic of my SR502 (before I wired it for the aforementioned zone 1 and zone 2).
Thanks,
Bill
Thanks,
Bill
Can you get a low voltage thermostat wire from the detached garage to the boiler? Then I would get the SR501 and do what @HVACNUT says above.Edward F Young. Retired HVAC ContractorSpecialized in Residential Oil Burner and Hydronics1
yeah I have a full tstat wire bundle going from garage into boiler room in the house.
No issues connecting to Isolated end switch in the house, even though I already have a wire from the two zones in the house connected to those end switch terminals?
Below is a pic of my SR501. It appears I already have a jumper in place, look good to you?
I'll use N/O 4 for the power to the circulator.
I'll run a low volt connection from bottom right N/O 6 and COM 5 to the end switch on the SR502?
Perfect.On a call for heat, the pump will be energized and the dry contact (5 and 6) will close, telling the boiler to come on via the isolated end switch on the SR502.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Thanks for all your help, I was able to take the N/O 6 and 5 COM from this SR501 in my garage into the house and on to the SR502 End Switch terminals. Worked like a charm. The garage in floor heat is ready for winter.
- 85.2K THE MAIN WALL
- 55 Biomass
- 73 Chimneys & Flues
- 129 Geothermal
- 3.3K Oil Heating
- 61 Pipe Deterioration
- 884 Plumbing
- 5.9K Radiant Heating
- 376 Solar
- 14.7K Strictly Steam
- 58 Water Quality
- 49 Industry Classes
- 89 Job Opportunities
- 28 Recall Announcements
