Question about bleeding Lochinvar Noble radiant
Novaman854
Member Posts: 9
I am almost ready to bleed, then fire up my Lochinvar Noble 110 combi. On my system, my radiant feed's come out of the boiler, up a few feet, then back down to connect to the manifolds. Did I set myself up for problems getting the air out? I have attached some pictures. Any advice is much appreciated!
The up and down should not be a problem. I cannot tell how the rest is piped from your pictures. Normally you set it up so that you can close a valve to isolate the supply from return and then power purge using the system fill valve."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
A fill valve with a fast fill function can help purge systems with high points like that. If you can isolate that loop and get a good 3-5 gym flow rate through it you should be able to push air out of any high points.
A 12 psi fill and the circulator alone will not generally purge air sufficiently. Some installers will add a coin vent or auto vent at high points. Is this the only ups and down?
Looks like a swing check on the autofill, a back flow device would be a better option, even on a private well system. It would better protect from the potential of boiler water entering the well water system.