reverse supply, return on indirect hwh
jerryb46
jerryb46 Member Posts: 60
any difference switching supply return on a indirect HWH. What problems could it cause?
  • STEVEusaPA
    Page 6
    https://www.caleffi.com/sites/default/files/coll_attach_file/idronics_17_na.pdf
    You want storage tank stratification for best and most efficient use. You also get more hot water with less energy.
    @hot_rod can explain it much better.
  • kcopp
    kcopp Member Posts: 4,678
    It would depend on the water heater.
    A coil type indirect if they were reversed may have some/ little performance issues. At one point HTP on their Contender WH had the install diagram listed one way and the photo in the same book listed the opposite.
    With a tank in tank set up there may be more of an issue.
    Why do you ask? Was your indirect piped "backwards"
    EBEBRATT-Ed Member Posts: 20,173
    loss of capacity