do TRVs balance your system for you?
weil_fail
Member Posts: 84
let's say you designed a system for a certain heat load, then you added insulation or an addition off of a room and your radiator is now incorrectly sized for the room. do Thermostatic Radiator Valves (TRVs) just automatically compensate for a wrong-sized radiator, or are there other factors to consider?
Thermostatic Radiator VENTS, not valves, will not balance a system that is out of balance. In the scenario which you describe, the best bet is to try a much slower radiator vent.Br. Jamie, osb
There's TRVs for two pipe systems as well as for hot water. Pretty sure it's valve, not vent.
I'm also thinking they behave differently with hot water.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
Oops. Well, right you are, @ChrisJ -- and we really don't know at this point what sort of system @weil_fail is talking about here. My bad.Br. Jamie, osb
I know how it is.
You automatically assume you're looking at the steam section.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
thanks for the info, dudes. I did mean hot water; sorry for not being clear.
is the best way to do a smart pump to get a condensing boiler with one built-in?0 -
I'm not aware of any mod-cons that come with a built-in boiler pump that modulates. The smart pump is installed to control the zone(s) after the hydraulic separator or low loss header.0
A minor caution: whether -- and how well -- a TRV can control a radiator or radiators depends a lot on how the system is piped. In a simple direct or reverse return system, each TRV will control it's associated radiator reasonably well. On a series piped system, a TRV will control all the radiators on that circuit -- which may not be what you want. And I would be of the opinion that the results on a monoflo system might be quite unpredictable...Br. Jamie, osb
With panel rads, for example, you can series a few of them and adjust the bypassing the H valve to do some balancing.
For the Euro market we build a balanced-able dynamic TRV to really accurately dial in a large system.
For a basic residential system the TRV function as Paul mentioned, with a ÔT cir works really well.Bob "hot rod" Rohr
Living the hydronic dream0