steam orifice

mikedo
mikedo Member Posts: 174
has anyone ever seen the orifice in a 2 pipe steam handle get plugged is it something i should be checking for.

Comments

  • JUGHNE
    JUGHNE Member Posts: 11,042
    Is the orifice in the valve itself or inserted in the valve spud union?
    No heat could be failed close rad trap.
  • Jamie Hall
    Jamie Hall Member Posts: 23,159
    Not saying it couldn't happen -- a stray piece of thread tape or something could get in there. But otherwise -- there's nothing in the steam which would do it.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • The Steam Whisperer
    The Steam Whisperer Member Posts: 1,215
    We've had one or two in the past 15 years on the couple thousand orifice plates we have installed.
    To learn more about this professional, click here to visit their ad in Find A Contractor.
  • mikedo
    mikedo Member Posts: 174
    i haven't taken it apart yet. I'm just trying to figure out my plan of attack to trouble shoot the system. its a two pipe dry returns with f&t traps .
  • Steamhead
    Steamhead Member Posts: 16,796
    What is the device mounted on top of the pipe in the pic? That's not where a trap or orifice usually goes................
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • mikedo
    mikedo Member Posts: 174
    thats what i think is an f&t trap on the return. I'm not considering the job anymore i can't pay him to let me do the work. he thinks i should work for free
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 1,951
    @mikedo. Don't know the circumstances but good for you. Value is not cheap. And there is no crime in making a respectable profit.