Honeywell Oil Intermittent Box
Joehawthorn
Joehawthorn Member Posts: 1
edited April 2020 in THE MAIN WALL
Thermostat calls for heat. Oil furnace will not go on till I tap the Honeywell's intermittent box.Then furnace is working Stays on till set temp is reached. Next time there is a call for heat it may or may not kick on till I go back downstairs to box that has ff ,tt terminals. Tapping the box gets furnace going again Never locks outside. Should I replace or clean contacts inside box? Thanks inadvance
  • Big Ed_4
    Big Ed_4 Member Posts: 3,530
    Are the wires and terminal tight ? Replace the primary control . Metal cover with plastic red button attached to the cover ? With that condition a small soldered in screw falls out holding the clapper to the board normally falls out with vibration .. Since it's a safety control just replace it .
    HVACNUT Member Posts: 7,451
    What brand and model (primary) box?
    Pics?
    Is it TT and FF only or is there a terminal block with R,W,C,G,Y?
    In either case, it seems like faulty contacts. The "tap" just helps them close.
  • STEVEusaPA
    edited April 2020
    C'mon @HVACNUT, it's a Honeywell Oil Intermittent Box...lol
    If someone is calling it that, they shouldn't be touching (or tapping, kicking hitting, throwing voodoo signs at) it, right?
    Robert O'Brien
    Steamhead Member Posts: 18,500
    Probably an R8184G which IIRC no longer meets Code. @Joehawthorn , you need a pro on this. Where are you located?