Honeywell Oil Intermittent Box

Joehawthorn
Member Posts: 1
Thermostat calls for heat. Oil furnace will not go on till I tap the Honeywell's intermittent box.Then furnace is working Stays on till set temp is reached. Next time there is a call for heat it may or may not kick on till I go back downstairs to box that has ff ,tt terminals. Tapping the box gets furnace going again Never locks outside. Should I replace or clean contacts inside box? Thanks inadvance
0
Comments
-
Are the wires and terminal tight ? Replace the primary control . Metal cover with plastic red button attached to the cover ? With that condition a small soldered in screw falls out holding the clapper to the board normally falls out with vibration .. Since it's a safety control just replace it .I have enough experience to know , that I dont know it all0
-
What brand and model (primary) box?
Pics?
Is it TT and FF only or is there a terminal block with R,W,C,G,Y?
In either case, it seems like faulty contacts. The "tap" just helps them close.0 -
C'mon @HVACNUT, it's a Honeywell Oil Intermittent Box...lol
If someone is calling it that, they shouldn't be touching (or tapping, kicking hitting, throwing voodoo signs at) it, right?steve1 -
Probably an R8184G which IIRC no longer meets Code. @Joehawthorn , you need a pro on this. Where are you located?0
Categories
- 112.8K All Categories
- 81.2K THE MAIN WALL
- 2.5K A-C, Heat Pumps & Refrigeration
- 37 Biomass
- 394 Carbon Monoxide Awareness
- 2.7K Controls
- 1.4K Domestic Hot Water
- 3.8K Gas Heating
- 101 Geothermal
- 133 Indoor-Air Quality
- 2.4K Oil Heating
- 32 Pipe Deterioration
- 582 Plumbing
- 4.3K Radiant Heating
- 334 Solar
- 12.3K Strictly Steam
- 38 Water Quality
- 11 Industry Classes
- 53 Job Opportunities
- 8 Recall Announcements