R-22 to R-410A changeout
Any helpful tips on this changeout?
    pecmsg Member Posts: 7,064
    A vague question!
    Like for like
    Insure the line set is the correct size
    Blow out liquid and suction lines well with N2
    Triple evacuations
    HVACNUT Member Posts: 7,451
    Meaning you're not able to replace the refrigerant lines?
    Its 2020 and this is your first rodeo?
    If you're certified but green, the book learning should be fresh in your head on how to properly recover, flush and prep.
    Please NO Flush!
    ChrisJ
  • ChrisJ
    ChrisJ Member Posts: 17,389
    pecmsg said:
    Please NO Flush!
    Some habits die hard.........
    Why do you need to pour chemicals in the line set that can do more harm then good?
    The few oz of mineral oil in there does nothing. We learned that in the 90's with R-134A conversations.
    The biggest issue is the crap that returns to the compressor because of the cleaning ability of POE and bad install practices. A suction filter should be installed then removed in a few days of operation. Unfortunately they only get removed after there plugged!
    SuperTech
  • ChrisJ
    Speaking of,
    How do you get "tainted" POE out of a system? I.E. POE that's been exposed to a lot of moisture etc.
    Speaking of,
    Dump it and replace it. Even a 500 micron vacuum the moisture remains.
    How are you getting enough to worry about?
    First buy in smaller quantities.
    Second use what you need. I put some N2 in the can before resealing but also get rid of the can if not reused within a month.
  • ChrisJ
    > @pecmsg said:
    > (Quote)
    I'm not, just something I've wondered about. If it's all throughout a system what can you do with it.
  • SuperTech
    SuperTech Member Posts: 2,661
    What about using a flush kit when replacing a compressor that had the windings burn out? Some guys insist that it's necessary. I like the idea of replacement of the suction and liquid line driers after a few days better myself.
    ChrisJ said:
    > @pecmsg said:
    > (Quote)
    Just change the oil once.
    Moisture and POE is a concern but mostly from bad practices of leavening containers open. 3GS days.
    As far as working on systems unless you actually blow into the tubing or its raining out and the suction is facing up and open its a non issue. Make your repair change the drier and close it up.
    ChrisJ