Weil-Mclain Aquabalance F37
Options
yellowlt1
Member Posts: 2
I have a recently installed Aquabalance AB155C Combi that keeps getting intermittent F37, low water pressure error. I have a Filltrol tank system with an autofill valve at 12 PSI. The manual states the low pressure switch is set to 9 PSI +/- 2. It may well be that the pressure fill is slightly low, and the switch is on the high side, but the F type errors are supposed to reset automatically, and mine does not. I have to keep powering the system down. Thinking of getting a more adjustable autofill and setting to about 14 PSI. Any suggestions? Thanks in advance!
0
Comments
-
I'd ditch the fill-trol setup in favour of a pressure reducing valve with a backflow preventer and expansion tank. It will make purging the zones a lot easier. The tank may not be the problem, do you have a gauge you can check the boiler pressure with? Post some pictures of the boiler and piping if possible.0
-
I have an Amtrol tank, but it has the built in 12 PSI fill valve. That's why I'm thinking going with an adjustable one that has a gauge. maybe set it a little high..
0
Categories
- All Categories
- 85.7K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 49 Biomass
- 424 Carbon Monoxide Awareness
- 71 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 92 Geothermal
- 149 Indoor-Air Quality
- 3.2K Oil Heating
- 59 Pipe Deterioration
- 847 Plumbing
- 5.8K Radiant Heating
- 371 Solar
- 14.5K Strictly Steam
- 3.2K Thermostats and Controls
- 50 Water Quality
- 38 Industry Classes
- 47 Job Opportunities
- 15 Recall Announcements