speaking of thermostats and obsolescence
It might be a better idea to integrate the AHU and the radiators together so they can't fight each other, esp. if one of them has internet access (which is often seen as license to fiddle).
That said, this shows that as having standard thermostat wire names (W, R, etc.), so it should be a straight swap, although if a common is lacking you may have to add one.
@Leonard, check out page 4 of the attached PDF, it shows how to set the anticipator.
Do you have any info on the amp. draw of the actuator motor.0
There are no wifi thermostats that can operate w/o a common wire. If you have 3 conductors you golden, or if you can fish/pipe one to a new location for your wifi thermostat. That may be easy to do.
I would also suggest integrating the AHU and radiation into one control. If you can adjust the AHU with your laptop, it most likely is controlled by some type of BMS (building management system) which would most likely have a spare output to run a radiation valve.Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0 -
A series 60 honeywell actuator is two position drive open drive closed. This link may help
http://machineryequipmentonline.com/electric-equipment/electric-control-fundamentalsseries-60-two-position-control-circuits/0 -
thanks guys. Still struggling at this. Called honeywell and they were very willing but not so helpful unfortunately. I did find the manuals for the actuator but I guess I just don't get the how the thermostat wiring board is connected to the actuatorEBEBRATT-Ed said:A series 60 honeywell actuator is two position drive open drive closed. This link may help
The actuator has a 24v power source to TT. There is another transformer that powered the clock on the old cronotherm
The green and yellow wires come from a separate transformer to the clock. Any help would be great. This is one of the areas that stumps me.
Use the diagram in the manual for Series 20 wiring.
The Red wire to R with slider joining Rc.
The White wire to Y.
The Blue wire to W.
The 24v (Green and Yellow) from the secondary transformer cannot be used.
For WiFi you will need a Common (C) to power the thermostat. You can take it from the transformer that's powering T1,T2 on the actuator. I assume T2 is Common but double check.2 -
Exactly what he said. ____/\____Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0
Ok just now did this wiring. still a blank screen. As if there is no power to the stat. I have 24 across R and W wire.
Whichever terminal you connected the Common wire to (T1 or T2) try moving it to the other one. Verify which is the correct terminal by checking for voltage between R and T1, and R and T2. You want the combination that gives you 24V.All Steamed Up, Inc.
Consulting0 -
Thanks a bunch fellas. The issue was the wrong location of the improper wire if that makes any sense. I've been forced out of that space for the time being so the students can do exams. So on to the next thing. Thanks again.
- 50 Industry Classes