Where to check draft on this
Northupthere
Member Posts: 35
There is a glass and plate and a brass bolt with what looks to be a flathead inner.
https://streamable.com/oz0wf
The boiler didn’t have a front panel when I moved in I think the oil guy said it’s German if this helps
Make and model of boiler?
Make and model of burner?All Steamed Up, Inc.
Consulting0 -
The oil guy said it is likely a Buederus 115 and the burner is a Reilo 40. He was able to test the combustion. He didn't want to remove the glass for draft in case it broke.
86.5% eff.
10.50 dioxide
6.9 oxygen
draft in the exhaust us .01 or .02
Carbon monoxide is 10ppm
excess air is 40
There was also a bike tire pump looking device that he put in the exhaust and the paper was white he said there wasn't any soot or smoke0
That last one is a smoke test pump. Glad to know it was used. 0 smoke only on the paper. No trace. No brown marks. No moisture. 0.0. Like Bluto's GPA.
The brass bung is for the over fire draft test. Loosen the screw, connect manometer. I believe Buderus wants 0 to slight positive on the G115.
The glass isn't even needed and I'm surprised Buderus still uses it. It is a little fragile. The one one the G215 is round and a lot thicker.
There should be a matching front cover that slides on top and a screw on each side.
Edit: In another thread, why are you replacing the oil filter and bleeding the pump if you had a qualified tech on site in this thread. I'm so confused.0 -
I bought the house in a foreclosure sale I didn’t find the front cover in the house. Must have taken it for a souvenir. He did mention that a hose can go over the brass nipple to check draft but he didn’t have one and he said the exhaust draft and other readings looked good.0
The flame looks ok no? The window must be useful for having a look sometimes but I’m not sure why it’s there either0
- 119 Chimneys & Flues
- 165 Indoor-Air Quality
- 76 Pipe Deterioration
- 15.6K Strictly Steam