Flexible Gas Piping do's and dont's

Options
jmholt
jmholt Member Posts: 2
Had a question about when it is acceptable to use flexible gas piping and when it is not. One of my co-workers came across a commercial rooftop unit approximately 150,000 btuh on a job that was hard piped in 3/4 up to the gas-cock and then run in flex 3/4 to the gas valve (approximately 3 ft) and he wanted to know if it was up to code. Any suggestions or versions of the codes books to refer to?

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 18,189
    That would be legal as far as I know. Did they use a flexible appliance connector or CCST?

    I would rater have it hard piped if it was mine
  • jmholt
    jmholt Member Posts: 2
    Here is a picture he sent me. When I looked closer I could see his model- looks like a Lennox KGA240 which would almost double the btuh I thought he was working with. Pipe size may be 1” looks to be CCST
  • BillyO
    BillyO Member Posts: 277
    Not in NYC
  • Ironman
    Ironman Member Posts: 7,726
    CSST tubing cannot be used as a connector, but a listed and approved (manufactured) CSST connector can be.

    In other words, it has to be a manufactured one, not field fabricated from tubing.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    STEVEusaPAjmholtHenry
  • unclejohn
    unclejohn Member Posts: 1,833
    That would have been one union two 90's and two 6" nipples. Whats the world coming to.
    SuperTech
  • Henry
    Henry Member Posts: 998
    That is NOT an approved flexible connector. Also if you are in an area that has frost, drip pockets are prohibited because they can crack.
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 18,189
    CSST can't be used as a connector which is why I asked about that in my first post.

    He should have hard piped it. It's close enough to do it with nipples wouldn't have needed a threader.

    Not sure if I have seen appliance connectors rated for outdoor use but they must be available
  • GroundUp
    GroundUp Member Posts: 2,364
    Where's the regulator? There should always be 2# gas to the roof, regulated down at each unit
    CBRob
  • mattmia2
    mattmia2 Member Posts: 13,401
    I thought that was a power steering hose for a second until I realized it was a short piece of the type of csst that has a metal braid and rubber on the outside to try to keep it from getting perforated in a lighting strike.
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 18,189
    @GroundUp

    It's probably low pressure gas you can see the pipe coming up through the roof the main must be run indoors. Very common around here. A lot of cities and town don't have high pressure gas
    GroundUpJUGHNE
  • rick in Alaska
    rick in Alaska Member Posts: 1,491
    Unless I remember wrong, you can run csst directly to an appliance if it not a portable unit. At least I have seen a few done this way, and the gas company allows it. The line also has to be protected from damage. I can not remember if it is a gas code that allows it, or if it is a manufacturers thing that allows it. I don't have access to either one of those codes right now.