Laars Endurance!!
I believe many of the problems are from the original installation but does anyone have an answer to this?
I understand their parts are disappearing for this unit so that's another problem.
Last question what do you recommend? Its gas supplied, makes our hot water and pushes the hot water through baseboards to heat the room. When it works, is great. Ten minutes after i arrive into a cool house, turn it on and the house is warm. Just hate these regular semi annual breakdowns.
Just to make clear: it is now not responding to thermostat when i turn it down. Came in yesterday and the house was boiling.
Thank you0 -
Hard to say. Need to get a technician in there with a meter.
I'd start by disconnecting the thermostat. If the boiler still fires, it's a problem with the boiler. If it stops, replace the stat.
I don't usually see thermostats fail closed.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Hi @Alan(CaliforniaRadiant)Forbes I just had a Honeywell Vision Pro 8000 fail on the board. My Lochinvar would keep running even though I removed the thermostat from its base. Disconnecting the R wire stopped the boiler from firing. Replaced it with a new thermostat (Same make and model) and all was good.Hard to say. Need to get a technician in there with a meter.
I don't usually see thermostats fail closed.2 -
> @Le John said:
> (Quote)
End quote.
That comment would make one think that there was either a short in the base plate or by removing the R wire, you reset the boiler.
Changing the thermostat may have rectified the issue because you most likely changed the base plate also. The other thing that could have happened there is that you have a short in the thermostat wires and moving the wires around opened the short.
Or a Wi-Fi stat issue. There was a problem recently with Honeywell thermostats on the Wi-Fi models , where the heat wouldn't work properly and had to be updated via Honeywell thru your Wifi.0 -
Hi @icy78 - yes the issue was in the base plate. Tech Support at @taco helped me find this. To test - I ran the base plate directly to the Zone valve control with new wire and it opened the zone vale and fired the boiler. I removed the bad plate and installed a Honeywell Pro 2000 plate and it did not open the valve to fire the boiler. Only when the Pro 2000 called for heat the zone valve control opened to fire the boiler. SupplyHouse.com send me a new Vision Pro 8000 redlink thermostat and the problem went away.icy78 said:> @Le John said:
> (Quote)
End quote.
Or a Wi-Fi stat issue. There was a problem recently with Honeywell thermostats on the Wi-Fi models , where the heat wouldn't work properly and had to be updated via Honeywell thru your Wifi.2 -
I live in Manhattan too. Endurance boilers were very popular in our part of the world for their small footprint and easy venting. Since then, the Codes have made the way we were venting them largely illegal and they are known for frequent breakdowns. In my experience with these boilers over many years, they internal "anti-condensing valves" were problematic and required replacing, but there are other known and frequent failures. Many of the new wall-hung units are better replacements.Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes1 -
@ johnNY - I have several in operation in closet installation. 40 inch by 40 inch by 80 inch, Problem is they are on upper floors with no drains. Any quality non condensing units out there?JohnNY said:I live in Manhattan too. Endurance boilers were very popular in our part of the world for their small footprint and easy venting. Since then, the Codes have made the way we were venting them largely illegal and they are known for frequent breakdowns. In my experience with these boilers over many years, they internal "anti-condensing valves" were problematic and required replacing, but there are other known and frequent failures. Many of the new wall-hung units are better replacements.
Did check, it still runs without the thermostat connected. So likely not the thermostat. Yes thank you John NY and others' response. Yes our Endurances were put in closet and I am on 6th floor. They were vented to outside. Still lots of lots of problems right away! within 4 years and for last 11, every two years something goes wrong (throughout the individual units in building same issues): either igniter needs to be replaced because won't go on and in my case, keeps running. What needs to be replaced then? I could go through my tax receipts from years ago but maybe you know something. The endurance people said something like "the controller; TTT" ??? Not sure what they meant.
Then, for replacement, what company do you recommend for condensing heater that does for hot water and water in baseboard heaters?
So appreciative of your helps.
Abbo0
- 87K THE MAIN WALL
- 113 Chimneys & Flues
- 106 Geothermal
- 981 Plumbing
- 388 Solar
