Smart stat and hydronic heat
Gta
Member Posts: 151
Hi folks
What smart stat would work best for radiant heat? Are there any to avoid? I’m looking at getting all 3 replaced in my house thx Sean
Btw I’m currently running the rehau dual sensing digital ones
By radiant heat, do you mean a radiant floor or radiant ceilings? If so, the response time of that type of heat to changes in thermostat settings is on the order of many hours to days. I cannot recommend using a smart thermostat which is allowed to ask for setbacks on lack of occupancy, or even overnight, for such applications.Br. Jamie, osb
Radiant floor0
A radiant floor takes hours to days to change the space temperature. They are great at holding a constant, comfortable temperature.Gta said:Radiant floor
Therefore, I honestly don't know what a "smart" thermostat is going to do for you.Br. Jamie, osb
Thin slab radiant floor with lots of thermal mass.
Turned down the thermostat to 50 Deg F when leaving for the south for 3 weeks mid Dec, took six days for the boiler to light up at 50 Deg.
On our return took 2 days to bring house back to 70 +/- on our return.
Set it and forget it unless you will be away for a week or more.
Thx for the input....0
I just honestly don’t like the rehau stats ...they turn on the boiler with barley any temp drop... I was hoping the smart stat could allow me to adjust it ...0
The best setup for a radiant slab, if your system has the option, is going to be primary/secondary, with the secondary always on and a mixing valve controlled by outdoor reset and a floor sensor. The boiler would then be controlled at the boiler -- not with an in-house thermostat at all. If it's a mod/con you can get the thing to run in condensing mode (and hence very high efficiency) most, if not all of the time.
If you need to boost the temperature in one specific space from time to time, I'd suggest a separate zone with panel radiators (or possibly baseboards) controlled by a local thermostat -- I'd probably use a simple Honeywell, but there are others. Don't try to manipulate the temperature of the slab.Br. Jamie, osb
It’s a 23 kw lion electric boiler.... I’m not sure how I can make it more efficient0
A simple Tekmar 161 will be fine. Set it and forget it.0
Guys another question... I have a Erie boiler boss SR301. My question is I have 3 zones : with 3 separate pumps and 3 separate t stats.
The main house is priority. When it runs the other 2 will wait .
But If the other 2 happen to call for heat at the same time they run together...?😮😡 that can’t be right? Especially as one is the garage set at 11c and the other is my bonus room set at 20c
How can I set it to run only one pump at a time ?
Thx0 -
> Thx
What's wrong with two zones calling at the same time? The boiler doesn't care what the thermostat is set for. Priority zone is normally used only if you have a domestic hot water zone. Typically a correctly sized and installed boiler should be able to operate if every heating zone is calling simultaneously.0 -
Hmm good point , I only ask because I’m my mind it would be easier to heat 1 zone at a time .
Anyway I’m using only 90-95 * water the house/ zones are getting to set temp easily. At this temp only 1-2 elements are coming on ... if I set it any higher all 4 go on then shut off repeat over and over .
Anything wrong using such a low boiler setting? Thx0 -
I would get your automatic controls set up properly and make sure that all the zones are circulating all the time with primary/secondary piping, mixed -- using the outdoor reset -- to the required temperature. Then the boiler should run just enough to maintain the required heat input to the floors -- whatever that is. A significant advantage of an electric boiler is that it can run at whatever temperatures are needed.Br. Jamie, osb
- 87.1K THE MAIN WALL
- 58 Biomass
- 114 Chimneys & Flues
- 110 Geothermal
- 162 Indoor-Air Quality
- 71 Pipe Deterioration
- 393 Solar
- 55 Water Quality
- 46 Industry Classes
