new water heater venting question
sonicboomin
Member Posts: 11
I'm getting my water heater replaced. i was told the hood and vent used on my unit now was small for it(3 inches).
I have a chimney with liner installed. If new heater requires 4 inch vent and the opening to my chimney is 3, will installer adjust that? is that something that is common?
Ah... depends on the chimney liner itself (not the opening in the chimney). If the chimney liner is correct as to type and size, then the installer can adjust the connections.
If it isn't... you have a big problem.
You should verify the type and size of the liner in the chimney -- you may need to have a chimney sweep to do that -- before proceeding.Br. Jamie, osb
thanks for reply. not sure to be honest, chimney not used as fireplace as we dont have any, runs from center of house from basement to roof.
i have steam boiler and water heater connected to it from basement.0 -
Hi no, opening for steam boiler is much larger than 3 inches.0
A picture showing the whole set up would clear this up.0
i will take pic once im home. FYI new boiler is AO smith 50 gallon 40000 btu,
anyone know if 3 inches will work for that model?0 -
@sonicboomin
Flue pipes and liners are sized for each individual job. They are base on btu input of water heater, btu input of steam boiler and height of chimney and type and size of the existing liner
We would need all the information to do that, but that is up to your installer. 3" flue may be fine for the water heater0 -
I could be wrong but I think a natural draft water heater that normally can use a 3" vent has to be 4" under some conditions I think if vented with a draft assisted boiler0
Pictures??0
- 120 Geothermal