Unusually high steam bills
whi7723
Member Posts: 22
Asking for a neighbor....she has had her steam system (only heat) looked at by the PUC and two plumbers to try to address her high utility bills. They have changed the meter and a couple bad traps and nothing significantly changed the bill. House is a 950 square foot house with an unfinished basement and two bedrooms. Heat is set at 60. Using over 20 units of steam a month where I have a house of six on steam hot water and heat and use 11-13. Doesn’t seem right.
Where is this located?All Steamed Up, Inc.
Consulting0 -
Is that on district steam?0
Located in Minnesota. It’s on a City PUC steam system.0
Never been near district steam, only read about it.
However, there must be a steam to hot water heat exchanger, (aka steam converter IIRC), for domestic hot water.
Could there be a pinhole water leak on the domestic water supply side inside the exchanger. This would add to the condensate leaving the exchanger and passing thru the cond meter.
Isolating the steam from the exchanger and seeing if cond water continues to come out of the steam side might tell you. Even cooler cond temp while operating??
Just a WAG.0 -
District steam they usually dump the condensate0
Steam usage is based on the difference between the indoor and out door temperatures.
Other variables are insulation and Tightness of windows.
Need to know what is a steam unit? Steam is sold at 1000 lbs. of steam per hour.
1000lbs of steam equals 970,000 btus.
Need some other information to assist.
Type of steam system, pictures of the piping system and rate for 1000 pounds of steam.
JakeSteam: The Perfect Fluid for Heating and Some of the Problems
by Jacob (Jake) Myron0 -
But do they meter the condensate first? And the billing is based on the gallons of condensate passing thru the meter before being dumped?0
One of the more common ways of doing it. A leak sounds like a good possibility...JUGHNE said:But do they meter the condensate first? And the billing is based on the gallons of condensate passing thru the meter before being dumped?
The OP did state "heat only", so maybe no DWH exchanger for that.
But do they do a steam to hot water heat exchanger for these houses that might use hot water rad systems also?0 -
It’s a direct steam line from the City into the house. If hot water, there is a hot water coil. The meter is in the house. Not getting into too much on the insulation or steam unit. I was just curious all things equal we have the same system, her house is half the size of mine with half the amount of people and her bill is double what mine is. Looking for a couple top ideas. Don’t need a concrete answer.0
Could you get us some pictures, if not of the neighbor's, perhaps of your's. Major components including the meter.0
Bad steam traps and steam going out the sewer or roof vents?0
Here are some pics0
It’s a direct steam system...not a Steam fired hot water system.0
Stumped? Me too.0
So, the steam comes into your house from the utility.
It passes thru one or more pressure regulators, then does steam go directly to your radiators for house heat?
Then for faucet hot water at the sink does that come from what looks like a steam to water heat exchanger. Or is that device also supply hot water to the heating radiators?
How about pictures of your radiators showing both ends?
Just curious what does your 11to 13 units cost you per month?
And another possibility is that YOUR meter is not registering everything that passes through lt.
I agree. They fill with water and break all the time.0
The heat loss of the structure governs how often the heat runs. Building envelope, insulation amounts, home orientation regarding the sun and solar gain (shaded vs not), wind exposure, ranch vs 2 story, number of windows/doors, etc. Lots of factors come into play here besides the heating system, so directly comparing two dissimilar structures that are used differently is a crude measuring stick at best.
Your neighbor should look at the long term energy use year by year. Has it always been high or is it a recent phenomenon? If it's a recent development, all things being equal, then yes the heating system might be the culprit. But, it sounds like the usual suspects on the steam system were checked.
If it's always been high, then your neighbor should look at the building envelope improvements to reduce the heat loss.Burnham IN5PVNI Boiler, Single Pipe with 290 EDR
18 Ounce per Square Inch Gauge
Time Delay Relay in Series with Thermostat
Operating Pressure 0.3-0.5 Ounce per Square Inch0 -
I can't tell where that meter is in all that piping. Is it a small diameter steam pipe and it is measuring steam volume or is it measuring condensate? If it is measuring steam volume the pressure of the steam at the meter will make a huge difference in what volume it measures for a given mass of steam passing through it? It also seems if it is measuring steam volume flow rate and condensation in the meter at low rates will cause a lot of issues with accurate measurement.0
Steam volume....spins a wheel0
That means it very likely will measure a lot less if you can keep your usage to a slow steady stream vs a number of on/off high flow rate uses.0
- 76 Pipe Deterioration