Zone keeps heating when thermostat is off
cerbysam
Member Posts: 7
We have an 8 year old Lochinvar Knight Boiler. Gas. There are 7 zones. One zone on the second floor continues to heat the baseboard even when set on 46 degrees and turned off. We changed the thermostat and the Taco Power head on that zone but it continues to do it. The heating technician said there must be a wire rubbing in the wall and wanted to take out all the wiring to the second floor. I think the problem is at the zone valve. Is there any way to test it or fix it. Taking all the wiring out to the second floor would be a huge job and I don’t believe that is the problem. Thanks for any help you can give.
Which model Taco zone valve is it?
If you disconnect the wiring from the valve and it is still heating, it isn't the wiring.(unless it is a power close type valve).0 -
New problem or was always an issue?0
Have you checked voltage to the zone valve? If there's 24 volts, there's a problem with the wiring. If no voltage, there's a problem with the valve not closing all the way.
I'm saying the same thing as @mattmia2.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
This has been going on for about a year. The valve is Taco Power Head 555-050RP0
You mentioned a failed circulator that broke and passed some pieces. Your zone valve may have some junk that is not allowing it to firmly seat and close completely.
Possibly opening and closing it several times might pass the kidney stone. There may be a time delay to open and close.
If this does not work then possibly valve repair or replacement.
Another possibly is "ghost flow" thru the return piping, but that would have been there from the start.1 -
Would like to see a picture or two of your system if you can post them here. It would help.
A possible flow-control valve could also be the culprit?0 -
Unfortunately I cannot get it to insert the photos.0
@cerbysam, you can click on the document or photo icon in the tools panel above the message box to insert photos. You can also send me a message with the photos and I'll post them for you. Here are some more tips for using the forum: https://heatinghelp.com/forum-user-manual
President
HeatingHelp.com0 -
I did that but after I pick the image size there is no prompt to attach it to the message.
Thanks for any help you can give me.0 -
Ok, So no pictures.
@cybersam
The reason you have heat in that area when that area or zone is not calling for heat, is probably because there is a valve serving that zone that is not working properly.
This could be the zone valve? check valve? flow control valve?
Any one of these, or a combination of these could be the reason. If the wiring is not at fault this is where I would look next.0 -
What is your city and state?8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
There are 3 wires going to the zone valve .a white and a red coming from the thermostat and a green wire. What is the green for? And what will happen if I disconnect it. If I disconnect all 3 wouldn’t that eliminate the thermostat being the problem0
Thats exactly what you should do, disconnect all 3. You either have a mechanical issue within the valve or a wiring issue. The first step should be to figure out which.cerbysam said:There are 3 wires going to the zone valve .a white and a red coming from the thermostat and a green wire. What is the green for? And what will happen if I disconnect it. If I disconnect all 3 wouldn’t that eliminate the thermostat being the problem
The 3rd wire is a powered end switch which is is a little confusing."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
If I understand the problem correctly.
If you have multiple zones hot water can flow backwards up the zone that is not calling for heat.
Install a check valve at the lowest point of the affected zone before the returns come together and enter the boiler.
This will stop any back feed that is occurring.
Jake
Pictures will be more helpful.Steam: The Perfect Fluid for Heating and Some of the Problems
by Jacob (Jake) Myron0 -
Did the problem start after you had the broken circ pump replaced?
IIRC, you mentioned pieces broke off of the pump?
Note: I thought I read about the pump in one of your prev postings; Perhaps I read the wrong post.0 -
Yes0
Thank for the information on the back flo. Will check that.0
- 120 Geothermal