Boiler return line - ghost flow
Jonn2018
Jonn2018 Member Posts: 29
edited December 2019 in Thermostats and Controls
Hi all have a bit of a strange hearing issue going on. Seems when Zone 1 is on zone 2 gets very hot. However when Zone 2 is on zone 1 does not get hot at all. The system has taco zone valves the guts for zone 2 were changed out thinking it was stuck in open position but problem continued. Also zone 1 and 2 have separate supply lines and zone valves. But only one return line as shown in the circle in the drawing. So I think we have a “ghost flow”. I think zone 1 return instead of flowing to the basement reverse flows into zone 2.
  • Ironman
    Ironman Member Posts: 7,755
    How about some pics of the boiler that include its near piping and the ZVs?
    Bob Boan
    HVACNUT Member Posts: 7,009
    You replaced the zone valve "guts". Does that mean the actuator head?
    You probably need to replace the valve insert. Easy enough.
  • Jonn2018
    Ironman I’ll post the pics when I get home tonight.
    HVACnut yes what we replace was the zone 2 internals the electrical part we knew was not the culprit.
  • Jonn2018
    Attached are additional boiler pics of the supply and return piping
  • HomerJSmith
    HomerJSmith Member Posts: 2,652
    Could there be a wiring mixup?
  • Jonn2018
    From what I saw the wiring looks fine. As far the the Honeywell valves goes, each zone valve turns on and off when it’s called.
  • Jonn2018
    Modified pics